    New England
    I have got an APCX230-OO chiller with remote air cooled condensor we are new to this unit.System has been trippig out for years on safteys when unit has low load and outside temp is below 65°.I installed tattle tails across safteys ,unit tripped on high oil temp the other night control cuts out at 185°.Changed the oil about 4 weeks ago oil was dark brown ,open drive compressor.Wih the unit running @50% load oil temp is 148°,refrigerant level of indoor receiver is half full.I have not been able to see its operation with a low load and cooler outdoor temps.Any ideas?
    Oct 2001
    are all your condenser fans coming on at the start,and see about putting a time delay jumper on the LP for low load starts on cool days...also megerohm the windings on the compressor(s) and do and acid test if you still have oil samples from the pull.check the charge on the next hi-load day with all your condenser fans running,amps,line temps.O/A temp into the condenser at full compressor load hi/lo readings!verfy the chiller controller is it for return water or dicharge water when you set it?
    New England
    Oil was tested no acid,open drive compressor no motor problems.unit run great loaded problem is running it unloaded with lower outside air temp,condensor fans are staging
    Hampton Roads, Virginia
    Does it have a hot gas bypass?, If it is really tripping on high oil temp I'm thinking not enough compressor cooling because the suction temperature is to high.
    "There is plenty of room at the top because very few people care to travel beyond the average route. And so most of us seem satisfied to remain within the confines of mediocrity." -- Benjamin Nnamdi Azikiwe, first president of Nigeria
    "It's not the customer's job to know what they want." -- Steve Jobs
    New England
    Yes it does have hot gas by pass and I have believed that it is a compressor cooling issue.It also has discharge regulating valve and a bypass regulaing valve.Sounds like under unloading conditions 10% hot gas kicks in ,discharge regulating valve and a bypass regulaing valve cause R22 stores out in condensor ,hot gas bypass prevents low pressure manual reset control from tripping.The IVC condensor fan staging is pressure and temperature.The first fan come on @ 160psi/100diff the second fan cyles with the first @ 40°/6°diff and the third @60°/6°diff.
    Are you sure about 160psi/100psidiff, thats low, this is R22 right?
    New England
    Yes it is R22 and yes I find the setting troubling but the is what is listed on wiring print and also note is not to tamper with setting from Dunham Bush. But I think it is a miss print from 1987 that no one has changed.
    Jul 2000
    Guayaquil, EC
    D/B APCX...........
    The D/B APCX air-cooled packages typically have liquid injection oil cooling that are very sensitive to having a solid column of liquid to work right. It's possible that during your low load/lower ambient conditions that the condenser is flooding sufficiently to cause the receiver level to drop and lose a good feed to the liquid injection. Could be a plugged filter or strainer too.
    The discharge pressure and bypass (receiver pressure) regulator are your flooding controls. Make sure that they aren't in a battle with the fan cycling controls. If the fan controls are set too low, you can flood the condenser unnecessarily and run out of liquid. This would be my first guess.
    The HGBP is usually a fixed solenoid valve controlled by slide valve position switches set way below 50% load. I don't think that's coming into play here.
    Poodlehead Mikey would know all this better than me. Hey Mikey! Where' you at?
    low head pressure at low ambient or low load conditions will
    trip out unit constantly. raise the head pressure to around 200 lbs and you should be ok.
    test it chaeck oil pressure at 160 lbs then raise it to 200 lbs and see if pressure doesn't come up. also make sure your unloaders and hotgas is set properly.
    do not let unit run unloaded for extreme periods of time
    try to make it loadup every so often.
    New England
    My concern on the head pressure is the oil pump pressue it is an open drive pump.Oil pressure is on the high side.her is a shot of the equiment. http://www.pbase.com/onesidedcoin/founders
    Jul 2000
    Guayaquil, EC
    What's it shutting down on then.......is it high oil temp or low oil pressure?
    The oil pressure is the net difference between oil pump discharge and compressor discharge pressures. So long as you maintain adequate discharge superheat you should have good quality oil to pump.
    New England
    It shut down last Thursday morring 12:30 AM on high oil temp.
    Dec 2003
    Kenilworth New Jersey
    High oil temp is actually high dischagre temp on the air cooled screws as the location fo the bulb or sensor will tell you. Check all the obvious stuff dirty condensers and fan cycling settings etc. and you`ll find the answer.