Isn't the horizontal condenser coil 3-4' off the ground and the evaporator higher than a oil sump 3" off the ground? trapping? circuit pumped down before shutting off the unit? Gravity, temperature, etc, doesn't matter, there is always some migration when vapor refrigerant is in contact with a pool of oil. Just a little refrigerant boiling out of the oil upon start-up, has nothing to do with oil level anyway.
If a day goes by and you have learned nothing, I hope you got a lot of sleep.
sounded to me like they were only running for a couple minutes, after being tuned off for, I'm guessing, maint, and guessing again, without a pump down.
Possible, but I did not actually read that anywhere.. I guess in that scenario that would be a diluted oil charge, I would think there would be more going on....
I have seen TXV failures (rare) and liquid solenoid failures do some odd stuff, but normally the software is smart enough to figure it out and spit out an alarm...
I see where you were going now...Just a different road.
GT
If a day goes by and you have learned nothing, I hope you got a lot of sleep.
"When I look at the bottom compressor glass, I don't see the oil being splattered on the window. What I do see is some small bubbles swirling in the oil, and eventually the oil foams on top."
"The oil level is about half"
"I made the observation at the startup after an extended off cycle. This is the only time that both compressors on this unit will run together."
I still don't see anywhere they only ran for a couple minutes at a time....
I had explained what he observed in the first post....His description of what he saw is what I would consider normal...Providing it subsides and is at a constant level....Simply oil windage.....Unless there is very low superheat, I see no reason for concern...
The one recommendation I would have is to check all pressures and temperatures and compare that info to the RLA to identify a tired compressor with a large amount of blow by....
Otherwise....All good.
GT
If a day goes by and you have learned nothing, I hope you got a lot of sleep.
i had a Leibert 20 ton computer room system would not stop pumping down
compressor was in a vacuum and pressure switch was working properly
the system showed no alarm, i noticed it during a maintanance
after a few minutes on the phone with leibert tech support
they had me twist a small capacitor off of the control board with my needle nose pliers
it fixxed the problem, you gotta love working on thee things!
.