    Quote Originally Posted by GT Jets View Post
    I have seen TXV failures (rare) and liquid solenoid failures do some odd stuff, but normally the software is smart enough to figure it out and spit out an alarm
    i had a Leibert 20 ton computer room system would not stop pumping down

    compressor was in a vacuum and pressure switch was working properly

    the system showed no alarm, i noticed it during a maintanance

    after a few minutes on the phone with leibert tech support

    they had me twist a small capacitor off of the control board with my needle nose pliers

    it fixxed the problem, you gotta love working on thee things!



    .

  2. #28
    Join Date
    Oct 2002
    Location
    Lexington, NC
    Posts
    5,159
    Quote Originally Posted by Airmechanical View Post
    i had a Leibert 20 ton computer room system would not stop pumping down

    compressor was in a vacuum and pressure switch was working properly

    the system showed no alarm, i noticed it during a maintanance

    after a few minutes on the phone with leibert tech support

    they had me twist a small capacitor off of the control board with my needle nose pliers

    it fixxed the problem, you gotta love working on thee things!



    .
    I don't exactly love working on the things, but a lot of the alarms can be bypassed in the setup mode of the software.
    The main thing is to keep the main thing the main thing!

    If "the grass is greener on the other side", it likely has been fertilized with Bull$hit!

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event