Results 1 to 7 of 7
  1. #1
    Join Date
    Oct 2005
    Posts
    174
    Post Likes

    TXV inlet Screen Stopped Up--30 OVE -TXV

    I have attached a Photo:
    This is a TXV-Sporlan-OVE 30 Ton--out of a Liquid Chiller--The Old Liquid Drier was a Sporlan 307---The Felt looking Debris--Would it be Possible for part of the Old Drier to have come Loose or could have some Foreign Material made it through the Drier---Anyone Experience this in the Past??
    Thank You.
    Attached Images Attached Images  

  2. #2
    Join Date
    Nov 2000
    Location
    Hoggtown! Toronto, ON
    Posts
    1,133
    Post Likes
    Maybe the last guy put too much heat to the filter/drier when brazing it in place. I've seen that happen. No nitrogen when brazing...
    "...refresh my memory. When did I start caring about this stuff...?"

  3. #3
    Join Date
    Sep 2008
    Location
    Cedar Rapids, IA
    Posts
    487
    Post Likes
    Quote Originally Posted by hvactech80 View Post
    I have attached a Photo:
    This is a TXV-Sporlan-OVE 30 Ton--out of a Liquid Chiller--The Old Liquid Drier was a Sporlan 307---The Felt looking Debris--Would it be Possible for part of the Old Drier to have come Loose or could have some Foreign Material made it through the Drier---Anyone Experience this in the Past??
    Thank You.
    Seen everything from rubber plugs that were not removed to dead birds. Moisture and POE oil can create some nasty crap too. One of the reasons why you should look thru a pc of pipe before its installed (even if you just removed the caps from it.)

  4. #4
    Join Date
    Nov 2009
    Posts
    387
    Post Likes
    I can't tell whats in there from the pic. I have had bi flow driers in YORK 6 ton heat pumps come apart in two different units. The stainless that holds the dessicant came apart into slivers and packed themselves into the indoor coil orifice. They were factory installed and were both Parker driers. However, this was years ago.

    I have also seen replaceable cores come apart in supermarket rack systems. So yes, it is entirely possible for driers to come apart for one reason or another.
    "Don't wish it were easier, wish you were better"

  5. #5
    Join Date
    Nov 2004
    Location
    Auburn, AL, USA
    Posts
    597
    Post Likes
    Someone used a gauze type core in a filter can?
    jt

  6. #6
    Join Date
    Nov 2009
    Posts
    387
    Post Likes

    catch all drier

    Here is a picture of a catch all drier like the 307. Check out the filter media material.
    Attached Images Attached Images  
    "Don't wish it were easier, wish you were better"

  7. #7
    Join Date
    Jun 2007
    Posts
    17
    Post Likes
    it lokes like the filter dryer did come apart. had the system ben opeaned or reparied befor

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech365 Virtual Event