Need LON AO expansion module
Seems like the ideal opportunity for an 'open system' but I can't find one. I need about 10-12 AOs on a controller. (5-6 would do if I double up).
-
05-09-2010, 11:21 PM #2
Professional Member
- Join Date
- May 2008
- Posts
- 290
Auslon do 1 with 4 AO's, Auslon AO module
Dazza
-
05-10-2010, 02:17 AM #3
Here is one that has 6 universal I/O + 2 relays.
BAS Remote
Embedded web page configuration that is built on the Sedona framework. Doesn't communicate LON, but it does Sedona SOX, MODbus, BACnet. If your using a JACE or such you have multiple options to integrate to.
kontrol out"Can't we all just get a Lon?" - Garry Jack
"BACnet: integration or interrogation?" - The Janitor
"Open protocols? You can't handle open protocols!" - Nathan R. Jessup
“What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE
-
05-10-2010, 05:14 AM #4
Professional Member
- Join Date
- Feb 2008
- Location
- Purcellville Va.
- Posts
- 653
http://www.loytec.com/index.php?opti...=283&Itemid=17
I don't think it has been released yet. But it should be soon. The I/O modules are hot swappable. I saw it at AHR this year and it looks very nice.
-
05-12-2010, 11:14 PM #5
I did run across these. Very interesting!
https://www.lonmark.org/certificatio...N-PRG12A-0.pdf
http://www.leopardcontrols.com.au/pdf/EC-12.pdf
What would I program the JCI with? I've done some FX with FXtools before. I'm putting DDC on a 10-12 zone multizone unit. It's a shame to have to put 3 controllers on because you only have 4 AOs!
-
05-13-2010, 03:25 AM #6
-
05-13-2010, 10:53 AM #7
Banned
- Join Date
- Apr 2010
- Posts
- 28
adder to Ninax...and programmed with LNS or AX.
Controls out.
-
05-14-2010, 03:54 PM #8
Professional Member
- Join Date
- Oct 2007
- Location
- England
- Posts
- 144
lon AO card
I'm not sure if you want a pure output card only or some form of control strategy included.
If you just want an output card, then Honeywell do an 8 AO card called an XFL822. This also needs a base to plug into called XS821-22.
I use these and they work fine.
-
05-17-2010, 08:02 PM #9
Good job Keith. I am wondering how they are set up though. This will be the first job I have done without a Jace. There will be just controller-controller Lon. I heard you can set up a 'ghost' station in R2 and bind the links. I just need a space temp and an AO per zone; programming can be done in another controller. I'm not sure what to with a 'plugin'.
http://specifyhoneywell.com/system/l...pdf?1267651383
-
05-19-2010, 05:17 PM #10
Professional Member
- Join Date
- Oct 2007
- Location
- England
- Posts
- 144
You will need a LON database set up if you want to use the plugin.
This should be no problem if you are using Lonmaker or something of that ilk.
If you are trying to configure the device with some program like NL-util or whatever which just reads and writes raw data to the NCI points then I might be able to guide you.
How do you intend to make the bindings between the cards and any controller?
You mention that you are not using a JACE this time. You could use a JACE to configure them though not?
I know the Lon interface dosent usually work from within your laptop when running AX workbench, but for ease a physical JACE could discover the card and the NCI's could be written to from this.
Tell me more


Reply With Quote