Trane Intellipak Question
I have a 50 ton Trane RTU with the Intellipak system that gives me a high supply air pressure alarm everytime it comes out of night set back. It is programmed to only go into set back 3X's a week for VAV calibration purposes. After being manually reset it runs fine for days, up until the next scheduled set back. I should also mention this unit has the inlet guide vains on the blower. They seem to operate fine after a manual reset. Any ideas what might be causing my unit to go off on high supply air pressure?
-
05-09-2010, 05:58 PM #2
Are they trane vav's? The vav's must close in order to calibrate, maybe the fan can't back off enough to prevent tripping the high static switch.
-
05-09-2010, 06:16 PM #3
Regular Guest
- Join Date
- Aug 2008
- Location
- Hbg., PA
- Posts
- 11
They are Trane VAV's. The indoor blower completely shuts off in night set back to allow for calibration so this shouldn't be a problem.
-
05-09-2010, 07:44 PM #4
Professional Member
- Join Date
- Sep 2008
- Location
- Delaware
- Posts
- 243
Is this a new or old problem? Are you connected to a Tracer/Summit system? Have there been any programming changes made about the time this problem started? Have you checked the Hi static cutout setting?
-
05-09-2010, 08:17 PM #5
Regular Guest
- Join Date
- Aug 2008
- Location
- Hbg., PA
- Posts
- 11
It is connected to a Tracer system and is a new problem. The high limit for the supply air pressure cutout is set at 4.0 iwc. What other settings in the Human Interface Module would give me this problem?