    Quote Originally Posted by ascj View Post
    So a little update.....
    So I got back there today. Removed the gas. Come to find out the cap tube was wrapped around the entire suction line(hence why they said it was 168" and I only guessed 60"). So I purged with n2, and unsweated cap out of coil. Cut the drier and compressor out. Blew through both coils with n2. Replaced the oil in the compressor. I installed the new drier and .036" x 168" cap, just like I took it out. (Also checked cap with a #64 bit after I cut it) Sweated everthing in, while purging n2. Weighed 8oz of 404a in. Still running like there is a restriction. Compressor overheating.

    Suction 15.8psi
    Discharge 222
    Liquid 220
    Suction 73 degrees
    Liquid 86 degrees
    Box temp 80 degrees
    Ambient 84 degrees

    Any ideas?

    BTW- I hate doing favors for friends.
    Head pressure looks low for that ambient.

  2. #41
    Join Date
    Sep 2007
    Location
    NH
    Posts
    918
    Quote Originally Posted by ascj View Post
    I jumped it out.....because the fan wasn't kicking on. I checked it by blowing some liquid on to it and it did close. But left it jumped out as I was checking it.

    I was a little hesitant about adding gas, since I was at 11 oz and the plate was 8oz. Would a couple oz really drop my sh that much? I was at like 95+ degrees SH.
    Take that jumper off the fans and let the evap get cold you got an 80 degree box blowing hot air over the coil. Chances are the pump is going to get really hot and could trip the ol.

    And SH doesn't really mean much at that kind of temp in the box you need to check it when your closer to opperating temps... I know you can't there but try taking that jumper off the klixon and see what happens at least your compressor will be alot cooler.

  3. #42
    Join Date
    Mar 2010
    Location
    QUEENS, NY
    Posts
    30

    Angry

    Quote Originally Posted by VTP99 View Post
    Head pressure looks low for that ambient.
    I"ve experince the same results after just blow the cap tubew that's there out
    With nitrogen. I don't understand why almost the same results occur. You went even further and removed the oil.
    My only question is did you clea, the coil good before start up.

  4. #43
    Join Date
    Mar 2007
    Location
    tx
    Posts
    983
    Quote Originally Posted by ascj View Post
    I did add 3 more oz to see what would happen. Not much change. It just won't run long enough with a such a high suction to the compressor.
    You could try false loading the box with some cold or frozed product. It might let tsystem get on down. Then take out the stuff you put in the box and replace it with cold product you are going to keep in the box. This is a long shot, and it probably won't work. And if it does, you still have a problem. It sounds to me that head pressure is still low for that load. You might even have a bad overload.
    Bad information is worse than no information at all.

    There are three kinds of people in this world. Those who can count and those who can't!

  5. #44
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    an 8 oz charge leaves no room for error

    there is a little bit of rocket science involved in propely getting an 8 oz charge in a closed system

    i sent you a PM



    .

  6. #45
    Join Date
    Mar 2007
    Location
    tx
    Posts
    983
    A hot pull down with a cap tube will look like an undercharged system as far as superheat goes. You will only be able to get a true assesment of charge when the unit pulls down to temp. I agree that the head pressure looks low for that ambient temperature espcially with that much load on the evaporator. I have a feeling that you either have a faulty overload, or a compressor that has some fatal mechanical damage.
    Bad information is worse than no information at all.

    There are three kinds of people in this world. Those who can count and those who can't!

  7. #46
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,092
    A few questions I have. Don't have much experience with cap tubes. Would the suction be that low with such a high load on the evap? I'm thinking that that it could be because the cap tube is just a pressure drop. But on the other hand you would thing that the suction temp would drop pretty quick, with no product in the box. Btw......I did run it for 45 minutes with the coil stat hooked up, keeping the evap fan off. Before I jumped it out.

    Also the compressor is definitely overheating. (I should have taken the shell and discharge temp....but it was hot as hell) Why wouldn't it with a 73 degree return?

    I also threw 2 bags off ice in there, to try to get the temp down to see what would happen. But it didn't drop the temp much......maybe 5 degrees or so.

    The way I evacuated and charge was.......I pulled a 200 micron vacuum through my gauges (didn't take long with such a small system). Both lines I had ball valves at the ports. I then hooked my tank up and bleed liquid up to the ball valves. I zeroed my scale that reads oz to the hundredth. I charged 8.13oz of 404a. I did add another 3.12 oz of 404a later to see what would happen.

  8. #47
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    5,175
    ascj A question I have is how are you going to fix a cap tube system that is a freezer and with the same components be a cooler?
    IMO if it is for a friend you should have them pick what they want the most and go from there other wise it will run piss poor no matter what you do to it
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  9. #48
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    5,175
    I read Ice's link
    That M# must be a Freezer only
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  10. #49
    Join Date
    Mar 2009
    Location
    Colonie, NY
    Posts
    23
    low suction pressure and high superheat really sounds like a restriction huh. i always try to order oem capillary tubes. i honestly would rather work on a walk in box any day rather than a reach in cooler or freezer. theres nothin worse than changing out a cap tube and still haveing an issue.

  11. #50
    Join Date
    Apr 2010
    Location
    West Virginia
    Posts
    636
    I would agree with it being restricted. I use a IR gun to measure the temperature of the coils in the condenser, if the top coil is warm but the rest are cool and maybe even the last will be nearly ambient then you have a restriction.

    could be the filter, could be the cap tube.

    jim

  12. #51
    I have been seeing alot of cap tube systems and heard about adding supco s8 additive oil to system and it will help unclogg cap tube. My question is how do you add the oil to the system.

  13. #52
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    2,192
    Google this

    CPSTLJ2

    I dont know if supco will clean clogged caps , it may make it worse because it loosens debris wherever its found.

    Its basically kerosene

    Your best bet is to replace drier , and cut out 5 inches of cap tube because thats usually where they clog

    Cut drier open to see what the problem was..... Wax build up , or drier self destructed internally

    If it was wax , then you need to keep cond coil clean because its getting too hot