One of the contactor coils is bad. When the contactor tries to pull in it drops the voltage (or va ) in the control circuit. This drop "Hangs up" the other contactors and prevents them from pulling in. Search for the defective contactor, you will find it.
-
05-08-2010, 04:51 PM #29[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
05-08-2010, 05:13 PM #30
I have a few techs condemn contactors on Carrier's, because they pushed them in and they held. But they always locked out again.
The CLO's use a triac circuits. By pushing in the contactor, there will be enough current to hold them in.
-
05-08-2010, 06:05 PM #31
Regular Guest
- Join Date
- Apr 2010
- Posts
- 21
I'm a new member trying to help others, Anyway you have your control voltage mostly it is 24VAC. This how the CLO does the s'tats calls for cooling the contactor energized on terminal 3 also energize the CLO logic circuit, must see at least 1.5 amps or the module will lock out. If the sensing loop does not sense amperage its open the contact between 2 and 3 and close contact 2 and X locking out the unit until 24VAC reset. Most Carrier unit has this CLO to monitor one leg of the compressor circuit. good luck
-
05-08-2010, 06:54 PM #32
Professional Member
- Join Date
- Feb 2001
- Posts
- 355
I see where flange asked in an earlier post if transformer was tapped right.
Have not seen a response ,may have missed it.If so my apologies.
I have seen units do this due to transformer primary not tapped to proper voltage.Usually 208 v unit and trans is tapped to 230v.Doesnt sound like much but it makes a difference when pulling all your low voltage loads at same time.Works sometimes but not always.Has enough voltage to hold your
contactors in but sometimes not pull in last stage. Good luck.
-
05-08-2010, 07:11 PM #33
Professional Member
- Join Date
- Nov 2004
- Location
- Auburn, AL, USA
- Posts
- 597
Timebuilder at post #16 got the the best possibility IMO. Several others have chimed in on the CLO controls. Pushing in the contactors and then having them stay engaged makes it seem like the control voltage is weak at the contactor or the contactor is bad. What happens is that the CLO is reset when the contactor is manually pushed in and full control voltage is then applied to the contactor.
I thought the CLO should lock out if:
Too low or no amps on the monitored leg after a predetermined length of time allowed for start-up.
After start-up time, too low amps or too high amps on the monitored leg.
If the monitored leg wire is switched to the wrong compressor wire, the CLO can seem like a real PITA.
If a replacement compressor has a different amps from the factory original, the CLO often gets blamed.jt
-
05-08-2010, 07:46 PM #34
Pull the common on the CLO and see if she fires off...The CLO needs the common to lock anything out....Common pulled it uses the safeties as a control circuit...So it could potentially short cycle itself to death...
A Redneck temporary fix is to install a delay on break TDR on the Y1 and Y2 circuits and pull the common until you figure out WTFO...
GTIf a day goes by and you have learned nothing, I hope you got a lot of sleep.
-
05-08-2010, 08:02 PM #35
-
05-08-2010, 08:05 PM #36
-
05-08-2010, 08:08 PM #37
Professional Member
- Join Date
- Dec 2008
- Location
- caribbean
- Posts
- 76
have the tranformer been replaced? maybe the VA ARE TOO SMALL , LOOSE OR RUSTY CONECTION SOMEWHERE
-
05-08-2010, 08:10 PM #38
Professional Member
- Join Date
- Nov 2004
- Location
- Auburn, AL, USA
- Posts
- 597
-
05-09-2010, 12:40 AM #39
Ive seen this happen before when the wrong size contactors are used. Check the amp rating of the contactors. If they are suppose to be 30 amp and someone installed three 50 amp contactors you will loose controll voltage at each contactor.