Results 1 to 7 of 7
  1. #1
    Join Date
    Jun 2004
    Location
    Paterson,New Jersey
    Posts
    2
    Post Likes

    Question

    Carrier 06E compressors with two unloaders. I need the to know how to set both unloaders. Another thing is that this compressor runs unloaded but when it goes to loaded condition the amperage goes to 76 amps and tripped the compressor breaker. Why?

  2. #2
    Join Date
    Sep 2002
    Location
    Hampton Roads, Virginia
    Posts
    1,901
    Post Likes
    No where near enough information to even start to answer your questins.

    What refrigerant?
    What are you cooling?
    and a million more questions.
    "There is plenty of room at the top because very few people care to travel beyond the average route. And so most of us seem satisfied to remain within the confines of mediocrity." -- Benjamin Nnamdi Azikiwe, first president of Nigeria

    "It's not the customer's job to know what they want." -- Steve Jobs

  3. #3
    Join Date
    Mar 2003
    Posts
    1,877
    Post Likes
    should unload at 58lb suction for dx and 55 lb suction for chillwater. whats the rla, whats the water temp, etc.,
    piston could be stuck on the cylinder that has the unloader.
    need info.

  4. #4
    Join Date
    Apr 2004
    Posts
    161
    Post Likes
    Originally posted by klrogers
    No where near enough information to even start to answer your questins.

    What refrigerant?
    What are you cooling?
    and a million more questions.
    Second that.

  5. #5
    Join Date
    May 2004
    Posts
    245
    Post Likes
    Originally posted by willieos
    Carrier 06E compressors with two unloaders. I need the to know how to set both unloaders. Another thing is that this compressor runs unloaded but when it goes to loaded condition the amperage goes to 76 amps and tripped the compressor breaker. Why?
    If it pulls 76 amps when it loads you got more problems than adjusting the unloaders

  6. #6
    Join Date
    Oct 2001
    Posts
    6,962
    Post Likes
    overcharged causing the trip,probably was charged in the unloaded state,pull some liquid out to break the sight glass then load it up and clear the glass in the loaded state.let it settle out and adjust them with the unit stablized on the charge.

  7. #7
    Join Date
    Mar 2003
    Posts
    1,877
    Post Likes
    maxter correct. you cannot charge a system unloaded or if it has hot gas when hot gas is feeding. unit must be fully loaded to charge. load machine you then charge to around 8 to 10 degrees subcooling,sight glass will probably clear just slightly before subcooling reached.do not add more gas after design subcooling reached, it will not do you any good theres a problem.