    OLD Reznor HRX350

    I am looking for specs for an old Reznor HRX350 make-up air unit.

    The unit was discontinued in 1990. The company no longer has any literature on the product. I am guessing an input of 350MBH( )...looking for a rated output value.

    I am a newb to HVAC and need to provide specs for these units for comparison to replacement units.

    Any help would be appreciated.

  2. #2
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    5,935
    Quote Originally Posted by CAEQENG View Post
    I am looking for specs for an old Reznor HRX350 make-up air unit. The unit was discontinued in 1990. The company no longer has any literature on the product. I am guessing an input of 350MBH( )...looking for a rated output value.
    The company still has the literature. It's just not listed exactly like your model number. It shows on the bottom of page 1 of the attachment that its 78% efficient.

    So that would be 273,000 BTUH.
    Attached Images Attached Images
    Instead of learning the tricks of the trade, learn the trade.

  3. #3
    I run with it.

    I called them and they told me they have no specs for the old unit...so a major thanks for the help!