  1. #14
    Join Date
    Jul 2001
    Location
    Gold Coast of Connecticut
    Posts
    4,644
    Wrong oraface in TXV distributor.........you got the 134 one in there!

  2. #15
    Originally posted by Tranetech
    The top third of evap is frosting.

    ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

    The distributor tubes seem to be feeding evenly, so I don't think they are the culprit, but I am beginning to think you guys are right about an orifice problem after the txv.


    weird refrigerant distribution is in it??? (top third()

    is the defrost heaters working ?? complete/full cycle

    Don't interrupt me while i'm talking to myself