    Confused Superheat at the Compressor

    My Question involves the Total Superheat at the Compressor on a Packaged Liquid Chiller—I have been informed since it is a Packaged unit with a short Piping run—The Superheat will be close to the Coil Superheat of 12---I have been informed in the Past—No less than 20 Degrees Total Superheat at the Compressor—I have been informed—if a Refrigeration Panellist answers this it will be 12 Degrees Total and if a Airconditioning Panellist answers this it will be 20---We have been Setting 8-12 Degrees SH on the Coil and 20 at the Compressor—Thank you for your Time.

  2. #2
    Join Date
    Jun 2005
    Location
    Las Vegas NV
    Posts
    1,152
    Post Likes
    Check out this old post. You'll find all your answers. Post 35 is from a Copeland guy.

    http://hvac-talk.com/vbb/showthread.php?t=161476

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,720
    Post Likes
    you are a field technician...copeland and every other compressor manufacturer will tell you that you need 20F because you have crap equipment, spend 5 minutes on troubleshooting and you dick with the txv everytime you have a chance...well, maybe not you, but you get the picture.

    if you are a manufacturer...then compressor manufacturers will allow you less because you test everything many times over with NIST equipment and then you write it down in the IOM that you need to have 12F suction superheat (or whatever).

    that's the difference.
    When she gets lonely and the longing gets too much
    She sends a cable coming in from above
    Don't need a phone at all
    We got a thing that called radar love
    We got a wave in the air...radar love....Golden Earring

  4. #4
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    4,001
    Post Likes
    Read the IOM to get the proper superheat setting for whatever piece of equipment. We were turned down by Mcquay for warranty on a compressor on one of their chillers because our start up sheet it was set for 12 degrees and their manual said it should be 8, always check the IOM.
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned