Carrier Infinity – Which system?
I would like your opinion; I am replacing a 30 year old York system (3.5 ton/90k BTU). I am located in Central/North NJ; the house is 2100 sq ft two story with a cathedral ceiling plus a 800 sq ft finished basement. I looked at numerous manufactures and have decided to get a Carrier Infinity System because of the Infinity 3 stage furnace.
Option 1 ($ net of all rebates, incentives, tax credit)
Furnace: 58MVC080-120 (80k BTU, 95%, 3 stage)
AC: 24APA748 (3.5/4.0 Ton, 16 seer, 2 stage)
Coil: CNPVP4821
New copper lines
Humidifier: HUMLBP2417
Infinity T-stat: SYVTXCC
Labor Warranty: 5 years
Option 2 ($ net of all rebates, incentives, tax credit)
Furnace: 58MVC080-120 (80k BTU, 95%, 3 stage)
AC: 24APA542 (3.5 Ton, 14.7 seer, 1 stage)
Coil: CNPVP4221
New copper lines
Humidifier: HUMLBP2417
Infinity T-stat: SYVTXCC
Labor Warranty: 5 years
Which is the better configuration? Why?
My contractor favors Option 1 due to the 2 stage AC. I am concerned the increase in size (.5 ton) could cause downstream issues. What do you think?
I look forward to your feedback.Last edited by BaldLoonie; 05-03-2010 at 06:09 AM. Reason: removed pricing
-
05-02-2010, 11:16 PM #2
Not allowed to post prices.
I would definately go with the 2 stage, however that house shouldnt need a 3.5 ton unless poorly insulated in which case you would be better off to weatherize and get the heat/cool load down so you can install smaller equipment.
-
05-03-2010, 12:24 AM #3
Option 1, Due to a nicer compressor. That unit does not come in half sizes. The infinity will size it to the airflow needed. Just make sure you have Manual J (load calc). I don't know your conditions but sounds a little big.
-
05-03-2010, 09:56 AM #4
Professional Member
- Join Date
- Dec 2009
- Location
- Falls Church, VA
- Posts
- 24
When given the option between a Hundai or a Rolls, and money is not the option .......
Option 1 is definitely better.
-
05-03-2010, 10:42 AM #5
Professional Member*
- Join Date
- Mar 2006
- Location
- The South
- Posts
- 1,842
CSCM
I would want to see the load calculation on both heating and cooling. you might be surprised at the results.
IMO
-
05-03-2010, 12:15 PM #6
New Guest
- Join Date
- May 2010
- Posts
- 3
Thank you for the inputs and I would welcome more of your in sights on the subject.
Not one of the HVAC contractors that gave me an estimate did a load calculation, they simply look at was there, measured a few ducts and asked some questions. Since my current 30 year old system was very old expensive to run, I also had a 12k BTU window unit upstairs to eliminate the heat difference upstairs and save some dollars. I also added R30 to the attic this past fall, this winter was much better.
The difference between the two options is <$800.
Could moving to the 24APA748 (3.5/4.0 Ton, 16 seer, 2 stage) cause any downstream issues (icing, humidity, etc)?
Wouldn’t a two stage 3 ton unit be undersized?
-
05-03-2010, 12:21 PM #7
Professional Member*
- Join Date
- Mar 2006
- Location
- The South
- Posts
- 1,842
Wouldn’t a two stage 3 ton unit be undersized?
CSCM
only a correctly performed load calc will tell you. insist on it.
and if you want to, look at the load calc on the header on the frt page. I believe the cost is only $49.
IMO