    Carrier Infinity – Which system?

    I would like your opinion; I am replacing a 30 year old York system (3.5 ton/90k BTU). I am located in Central/North NJ; the house is 2100 sq ft two story with a cathedral ceiling plus a 800 sq ft finished basement. I looked at numerous manufactures and have decided to get a Carrier Infinity System because of the Infinity 3 stage furnace.

    Option 1 ($ net of all rebates, incentives, tax credit)
    Furnace: 58MVC080-120 (80k BTU, 95%, 3 stage)
    AC: 24APA748 (3.5/4.0 Ton, 16 seer, 2 stage)
    Coil: CNPVP4821
    New copper lines
    Humidifier: HUMLBP2417
    Infinity T-stat: SYVTXCC
    Labor Warranty: 5 years

    Option 2 ($ net of all rebates, incentives, tax credit)
    Furnace: 58MVC080-120 (80k BTU, 95%, 3 stage)
    AC: 24APA542 (3.5 Ton, 14.7 seer, 1 stage)
    Coil: CNPVP4221
    New copper lines
    Humidifier: HUMLBP2417
    Infinity T-stat: SYVTXCC
    Labor Warranty: 5 years

    Which is the better configuration? Why?
    My contractor favors Option 1 due to the 2 stage AC. I am concerned the increase in size (.5 ton) could cause downstream issues. What do you think?

    I look forward to your feedback.
    Last edited by BaldLoonie; 05-03-2010 at 06:09 AM. Reason: removed pricing

  2. #2
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    6,325
    Not allowed to post prices.

    I would definately go with the 2 stage, however that house shouldnt need a 3.5 ton unless poorly insulated in which case you would be better off to weatherize and get the heat/cool load down so you can install smaller equipment.

  3. #3
    Join Date
    Jun 2006
    Location
    Hastings, MN
    Posts
    417
    Option 1, Due to a nicer compressor. That unit does not come in half sizes. The infinity will size it to the airflow needed. Just make sure you have Manual J (load calc). I don't know your conditions but sounds a little big.

  4. #4
    Join Date
    Dec 2009
    Location
    Falls Church, VA
    Posts
    24
    When given the option between a Hundai or a Rolls, and money is not the option .......

    Option 1 is definitely better.

  5. #5
    Join Date
    Mar 2006
    Location
    The South
    Posts
    1,842
    CSCM

    I would want to see the load calculation on both heating and cooling. you might be surprised at the results.

    IMO

  6. #6
    Thank you for the inputs and I would welcome more of your in sights on the subject.

    Not one of the HVAC contractors that gave me an estimate did a load calculation, they simply look at was there, measured a few ducts and asked some questions. Since my current 30 year old system was very old expensive to run, I also had a 12k BTU window unit upstairs to eliminate the heat difference upstairs and save some dollars. I also added R30 to the attic this past fall, this winter was much better.

    The difference between the two options is <$800.

    Could moving to the 24APA748 (3.5/4.0 Ton, 16 seer, 2 stage) cause any downstream issues (icing, humidity, etc)?

    Wouldn’t a two stage 3 ton unit be undersized?

  7. #7
    Join Date
    Mar 2006
    Location
    The South
    Posts
    1,842
    Wouldn’t a two stage 3 ton unit be undersized?

    CSCM

    only a correctly performed load calc will tell you. insist on it.

    and if you want to, look at the load calc on the header on the frt page. I believe the cost is only $49.

    IMO