    What would be the highest acceptable suction line pressure drop, and lowest refrigerant velocity ( ft/minute ) @ +42 sst for R404A and R407C?

    [Edited by bayou dude on 06-14-2004 at 05:18 PM]

  2. #2
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,078
    I generally like to size for about 2#/100ft equivalent length of run for pressure drop The minimum velocity depends on on if you're running horizontally or vertically and how much unloading (if any) is involved......1500 FPM is a good starting point. Larger risers need higher velocities to "entrain" the oil for proper return.

    Speaking of "Trane", they seem to like pressure drops up to 6#/100 ft and velocities up to 4000 FPM.