    Hill phoenix screw rack.
    R-507. carrier scew compressors, o6trd and o6tado.
    combo rack, with hot gas defrost, liq subcooled.

    gentlemen,
    any experience on changing the oil on these screw racks and what is your service procedures to shut down and do the job. i also want to replace oil cartrides and strainer.

    i would appreciate if you share your experience.

  2. #2
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084
    It's pretty straightforward.
    If it's the rack I think you are talking about , there is plenty of isolation.

    You can shut 'em down for a while with no problems.
    Not really sure what you are asking.

    But I will say that, that oil is the worst . (on your hands I mean)

  3. #3
    Join Date
    May 2004
    Posts
    21

    F/U answer for Ned.

    Ned,

    basicly i would appreciate any of your experiences
    and any precautions on these r-507 screw racks.
    experiences with, carlyle, the Cem modules or anything else
    that you can think of to Watch out For.
    I am Going to Have my Journeyman Mechanic in 2 weeks replace all the oil and oil filters and all liquid and suction cores.
    My experience with screw Machines are with Bitzer compressors and a older R-22 tyler screw machine in vons.


  4. #4
    Join Date
    Aug 2000
    Location
    USA
    Posts
    4,995

  5. #5
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084

    Are you changing oil for maint,or for problems?

    I was working some a while back on one of the newer screws with the LON CEM (I think its called) and Comtrol.

    We were having "dirty filter" fails .

    Filters looked good , pressures good also. Turned out to be one of the transduc's was freaking out and making the module think it was losing oil pressure.

    There are certain conditions the module needs to see to keep the comp on line. If any of the parameters are too far out of line the module times out.

    The transducers can be verified by comparing the PSI to the volts and matching it to a chart (LON CEM guide).

    The bad tranducer I was talking about would jump around (volts wise) and trick the module. You would have to stare at it for a while to make sure it maintains its readings (again comparing it to the chart)

    Luckily I had an extra transduc from a comp we had changed the week before. The failure quit.

    Maybe you can get the chart or better yet the mini manual for the LON CEM from the link absrbrtek posted .

    It explains generally how the module operates and fails.

    We also had some factory wiring issues in the control panel.( Damn HillPHOENIX )

    That issue was 4-5 months ago and I've been breathing alot if freon lately so it's a little cloudy.

    Other than that the rack is sweet. The variable speeds make quite the sounds don't they?

    Hope that help at least a little.

    NED

  6. #6
    Join Date
    May 2004
    Posts
    21

    Thanks Ned.

    Ned,

    thanks for your reply.
    Yes this would be a scheduled PM for this RACK.
    This is a New customer and the rack is 3 years old.
    I just recieved a P.O to perform all the work.
    Field experience is priceless and this seems to be a really great tool( web site). I am new to the online thing so please be patient with some of my threads.

    Thanks,

    GM-1978

  7. #7
    Join Date
    May 2004
    Posts
    51

    as ned said...

    it is pretty straight forward with isolations that a journeyman can figure out.

    I think that is the same rack the Super Targets have?

    As far as carlisle compressors... You probobly already know this, but They don't like liquid AT ALL! Carefull...


  8. #8
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084
    http://www.carlylecompressor.com/PDF...06tstartup.pdf

    absrbrteks link is a good one ...here is the chart I was talkin' bout....very good reference...saved my butt

  9. #9
    Join Date
    May 2004
    Posts
    21

    Hill- Phoenix screw rack.

    Thanks Ned,

    for all your Knowledge and experience.


    GM-1978

  10. #10
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084

    Re: Hill- Phoenix screw rack.

    Originally posted by gm-1978
    Thanks Ned,

    for all your Knowledge and experience.


    GM-1978
    I'm definately no expert .
    I'm learning those racks also..but am happy to share my past headaches .

  11. #11
    Join Date
    May 2004
    Posts
    51

    carrier not carlisle

    sorry! I KNOW the carlisle, even screws are liquid prone more than usual to valve damage, but not sure of the carrier racks you spoke of. I did not read your initial post correctly!!

  12. #12
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215

    Re: carrier not carlisle

    Originally posted by stenfam
    sorry! I KNOW the carlisle, even screws are liquid prone more than usual to valve damage, but not sure of the carrier racks you spoke of. I did not read your initial post correctly!!
    He's referring to Carlysles.

    You'll be OK, just use good service procedures, print out the pdfs, and away you go.

    Factory wiring issues, Ned? C'mon.

  13. #13


    Here is what you'll look like once you change the oil cartriges on that rack.


    talk about some serious foaming yuk....