Page 1 of 2 12 LastLast
Results 1 to 13 of 17
  1. #1
    Join Date
    Nov 2003
    Location
    Wisconsin
    Posts
    452
    Whoops, started this thread accidently in res hvac........Now let's put it where it belongs.

    The facts as I know them minus a couple

    Box temp 43
    r404 system
    evap split 2 degrees
    41 degree temp exiting evap
    38 degree suction line temp at compressor
    suction = 80+/-
    high side 250
    ambient = 85
    Cose suction and system takes approx 3 minutes to pull down to 0 psig. Lock down high and leaks back to 20 psig in about 2 min. Changed one condensor motor. Evap and condensor both clean. Dang thing acts like overcharge but nothing been added. Been running for 4 years till this. System is a Bohn with the beacon system attached. Small box (8x10), w/15 ft of line. Overnite, will not go below 39.

    Any thoughts? I got pulled off for some A/C while boss went to look at this one after I had started. He's baffled, but as a result I don't have info on subcool and condensor splitt, etc


    Thanks

    Rango

  2. #2
    Join Date
    Dec 2000
    Location
    Flat Rock, NC
    Posts
    335
    Is compressor running constantly? Superheat readings are taken directly off of beacon board located in box on front of evap.. Superheat should be running 8-10 deg. Instructions for board are inside cover. This board is somewhat self diagnostic and may be flashing an error code(probably a bad sensor). Make sure if you replace sensor(s) you use the latest version from beacon. These sensors are prone to water intrusion and failure. These units are tricky to diagnose if your not familar with them, as they try to refrigerate even when they sense a problem, rather than shutting down w/total loss of refrigeration.

  3. #3
    Join Date
    Apr 2002
    Location
    most of the time in the Philippines
    Posts
    1,206
    You can download a service manual from Heatcraft's website.

  4. #4
    If your getting no real split across the unit cooler ... then your not feeding any freon.
    And if your not feeding freon, your NOT refrigerating.

    Hmmmmm.... bad powerhead on TX?
    Totally pluged screen on inlet to TX?



  5. #5
    ..and ..... if this sucker is running and not refrigerating ... why hasnt the low pressure control opened up and stoped the unit from running?


  6. #6
    Join Date
    Nov 2003
    Location
    Wisconsin
    Posts
    452
    This thing has an eletronic expansion valve on it as per the Bohn website. Stepper motor regulates superheat based on superheat sensor mounted on suction line and inputting to logic control. Are definetly getting some refreration effect as when you raise box temp to say 50 degrees, you will get a small split. Unit will cool (excruciatingly slowly). Boss walked into it this morn and it was 37 degrees after working all night. That's the setpoint and unit still would not pump down and cycle off. No solenoid valve on this systm. When box gets down to temp, stepper motor shuts off refrigerant supply through EV. Gotta be the electronic expansion valve stuck and not moving or weak compressor will not move refrigerant throught the system and pump down when through. I'm leaning towards the latter as the compressor takes approx. 2 min just to pull accumulator to 0 Psig.

  7. #7
    Join Date
    Feb 2004
    Location
    puerto rico
    Posts
    121
    hello friend; you said the suction be back in 2 min, ok what time take to be in 35psig

  8. #8
    Join Date
    Nov 2003
    Location
    Wisconsin
    Posts
    452
    LPCO set at 0 psig with 20 psig diff. Close suction valve and pulls dow3n to cut out. Takes app. 2 min +/-. At cutout, close liq valve. Leaks back to cut in press (20) within a couple of min.

  9. #9
    Join Date
    Feb 2004
    Location
    puerto rico
    Posts
    121
    hello friend; you better be sure,about the liq-valve is worlking,(that valve receive volt dc or ac) example 120volt 220volt or 0 to 10volt,dc

  10. #10
    Join Date
    Nov 2003
    Location
    Wisconsin
    Posts
    452
    No liqid solenoid valve. I'm talking about the liqiud dervice valve.

  11. #11
    Join Date
    Feb 2004
    Location
    puerto rico
    Posts
    121
    hello friend; the valve that you tell me,use or not use voltage.

  12. #12
    Join Date
    Nov 2003
    Location
    Wisconsin
    Posts
    452
    Sory Clave, thought you were talking about the service valve. Expansion valve is O-5v.

  13. #13
    Join Date
    Feb 2004
    Location
    puerto rico
    Posts
    121
    hello friend; maybe you has problem between (exp val, some sensor or board) do a visual check in wires loose by some vibration.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •