Results 1 to 13 of 16
    Midwest
    [Edited by midhvac on 06-07-2004 at 08:21 PM]
    Mar 2002
    Richmond, Virginia
    It sure looks lonely up there! Must not be much conditioned space below.
    There is nothing more frightful than ignorance in action....Mark Twain
    Apr 2004
    Maryland
    i like the trap on the electric wire. Very ingenious
    SouthBlomfield,OH (outside columbus,Oh)
    sure hope that exposed high voltage is uv rated. If not someone will be back. In some areas they will not let you tie high voltage(230v) to a low voltage wire unless it is sheilded.
    Midwest
    Sorry, the pics aren't too clear, but it's 3 phase and the wires are in aluminum tubing. The stat wires are.... were taped to the tubing. The tubing goes into a larger conduit down through the roof which isn't sealed, so rain goes in it.
    The unit which they replaced was sitting on those plastic legs, but they didn't bother putting anything under the Rheem.
    Most of the insulation on the suction line is missing. Discharge line from unit (5 ton) comes out of unit at 3/8 and immediately goes into 5/8. Single story building, 40' lineset.
    Looks like they got a little close to the flue cap with the crane
    [Edited by midhvac on 06-07-2004 at 09:58 PM]
    Arizona
    When you said "discharge line" did you mean the "liquid line"?
    If that thing jumps form 3/8 to 5/8 holy sheet man. That's one hell of a receiver! It must hold a few extra pounds!
    ;-P
    Cincinnati
    They just sat it on the rubber roof? You'de think after a quality job such as that the old unit would still be up there cause they were to lazy to get rid of it.
    Apr 2001
    Camel City, NC
    Niceeeee
    So who mashed the B-vent cap down? Was there a call or were you just cruising the roof?
    Be safe not fast. body parts don't grow back
    Alberta Canada
    Cool
    Too many times, the motto "When you get time...Hurry" gets in the way of quality workmanship.
    Looks to me like it has 3/4" suction and 3/8" liquid line.
    Midwest
    The liquid line is actually 5/8, but looks small because the suction line comes out of the unit at 7/8 and immediately goes into 1 3/8
    I was actually called to fix the other old Lennox unit (thank goodness). Didn't want to see the pressures on the Rheem. Most of the rubatex (about 20 ft) is off the 1 3/8 suction line.
    Apr 2003
    Iowa
    Maybe the reinstall will be better when they move it to fix the holes the unit creates in the roof membrane from vibration.
    There are 3 ways to do anything in life; Good, Fast, Slow: You can pick any 2.
    Houston,Tx.
    Talking
    midhvac, come now be honest with us you know your sat on the vent cap because you were laughing so hard you could not continue to stand up.
    Apr 2004
    Thumbs down
    No oil trap for that distance. I know from experience.If his evaporator is even 4 ft down hes done like dinner.