    Confused Oil System Fault (Trane RTAA Chiller)

    I have a Trane chiller model # RTAA0704XN01S300BN, Serial # V02J06868. Both circuits have repetitive failures from "oil system fault". Both oil temperature sensors have been replaced and the condensers have been thoroughly cleaned. After cleaning, seen reduced failures with circuit A, but no change with circuit B. Also, noticed that circuit A has entering oil temperature of 110.4F and circuit B has entering oil temperature of 75F. Past problems: Circuit "A" was showing below freezing temperature on oil, but problem was remedied after oil temperature sensor was replaced. Any input on what could be causing this?

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by randystoker View Post
    I have a Trane chiller model # RTAA0704XN01S300BN, Serial # V02J06868. Both circuits have repetitive failures from "oil system fault". Both oil temperature sensors have been replaced and the condensers have been thoroughly cleaned. After cleaning, seen reduced failures with circuit A, but no change with circuit B. Also, noticed that circuit A has entering oil temperature of 110.4F and circuit B has entering oil temperature of 75F. Past problems: Circuit "A" was showing below freezing temperature on oil, but problem was remedied after oil temperature sensor was replaced. Any input on what could be causing this?
    assuming the oil temperature sensors are correct...you need to look at the saturated evap temp and compressor temp sensors. if they are wrong, then you could flood back (the compressor won't care), however, you will be putting liquid refrigerant into the oil separator. as the liquid boils off, it pre-cools the oil before going into the oil cooler portion of the condensor. this makes the oil temp colder than the saturated condensing temperature...which is the reason for the diagnostic.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  3. #3
    Join Date
    Apr 2009
    Location
    Diberville, Mississippi
    Posts
    28
    Post Likes
    Thread Starter

    Thumbs up Fixed!

    Your diagnosis was exactly on the mark! The "oil system fault" failure is not a problem anymore. Thanks for the help!!

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •