    Leaking liquid Solenoid Valve

    Correct me if I'm wrong, but when a unit goes into a pump down, I should not see any movement in the site glass, as well as a very, very, small rise in low side pressure, correct?

  2. #2
    Join Date
    Mar 2005
    Location
    Portland
    Posts
    285
    Post Likes
    what is the cutout setpoint on the pressure control? it's fairly common to see a small increase in pressure on the suction side if the cutout point isn't close to zero. a leaking solenoid valve will most likely cause suction pressure to continue to rise and the unit to repeatedly cycle off and on.
    you will attract more flies with honey than with vinegar, but you can attract the most with a dead cat

  3. #3
    Join Date
    Mar 2015
    Location
    Hamersville, Ohio
    Posts
    62
    Post Likes
    Heatermanbob,

    The setting is 6PSI (18/12). The "bleed through" is very slow, & as far as "cycling"? It's not doing that. The air bulb stat is pulling the unit down to 37 degrees, which in turn is pulling in the valve, for the pump down. Much of this system is original from 1999, yet, many people have worked on this cooler, & other components of the store, & "Hacked" many repairs. Sporlan Tech is telling me that this valve is for an 8 ton application, & "to big" for the compressor /system. a 3 door walk in, at the same store, had the same size valve on it, but, that system was "Hacked so badly", that it failed, & had to be replaced. This valve is on a 3 evaporator walk in cooler, where I replaced the compressor, failed Contactor, time clock, & one evaporator motor. I told the customer about this valve being over sized, when I had the system down, & installing the correct valve would've been easier. He wanted his cooler going, & said he'd "worry about it later".
    My concern is seeing this "steady trickle" in the site glass, "IF", I am to have a 100% closing of the valve.

    My customer is from Ethiopia, & on one hand proclaims that "he is poor", & then later speaks of his vacations, private school for his kids, & the amount of credit he can get for opening up a restaurant in the same building. Our agreement is that he gets a discount, based upon my doing ALL of his HVAC/Electrical/Refrigeration/Plumbing & Restaurant equipment, so I want to be sure of dotting all of my "i's & t's". All of this work I did on this cooler, was done by a contract, & specific to the Condenser repairs. Any other work, which is referred to in the contract, such as cleaning all of the coils, adjusting the TX Valves etc., is to be additional.
    So, a "small increase in pressure", you consider "Normal"? Does that include new valves also?

  4. #4
    Join Date
    Mar 2005
    Location
    Portland
    Posts
    285
    Post Likes
    any liquid or saturated vapor downstream of the solenoid valve is going to boil off and increase pressure once the pressure switch shuts the compressor off. not convinced you have a leaking solenoid valve if it's not continuously increasing pressure and short cycling.
    you will attract more flies with honey than with vinegar, but you can attract the most with a dead cat

  5. #5
    Join Date
    Sep 2002
    Posts
    4,249
    Post Likes
    Is the valve close to the Evaps,as it should be?

  6. Likes DavidDeBord liked this post.
  7. #6
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    2,411
    Post Likes
    Small increase normal, if it is enough to cause it to attempt pumpdown, it might be leaking at the solenoid valve or back into the discharge side thru valves. I would pump it down, isolate the discharge, and make sure the comp cannot restart and watch your low side. A slow leak on the solenoid might also show up as temp diff over it form in to out.

  8. #7
    Join Date
    Mar 2015
    Location
    ARK.
    Posts
    1,034
    Post Likes
    I would be concerned if the unit has multiple,3-4 pumpdown's on 1 off cycle with a long line set.Close couple and either the lo pres sw is not set low enough or it's by-passing someplace.Do as buford said and find the cause.

    As far as the "customer". Well,That goes without saying bro.We all been there,seen it.Either hold the Hand or fold.

  9. Likes buford, Carbent liked this post.
  10. #8
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,578
    Post Likes
    If its not cycling , dont worry about it
    If SH looks good , fughedaboudit

  11. #9
    Join Date
    Mar 2015
    Location
    Hamersville, Ohio
    Posts
    62
    Post Likes
    Whelp,..... somehow, when I went to post my reply, I got informed that I didn't have permission to post. Then I saw that I had to log back in. When I went back to post my reply, to the last 5 comments, it was gone!
    I don't understand this, cuz, I only went to the coffee pot, & then called the dog in from outside (less than 5 minutes.).
    I've got things to do in the Physical world, & I'll have to get back with Ya'll tonite.

    Heatrmanbob, Coolperfect, Buford,Mr.kelly, & Snapperhead,.... I appreciate your input.

  12. Likes coolperfect liked this post.
  13. #10
    Join Date
    Mar 2015
    Location
    ARK.
    Posts
    1,034
    Post Likes
    It seems to happen around here.
    I accidentally double post because "something" is trying to do "something".
    When this happens,I copy my intended post and when it makes up it's mind,paste my original response back in.
    Why can I post in AOP with no * ? Can so whatever. Yes I am qualified but no *.

  14. #11
    Join Date
    Mar 2015
    Location
    ARK.
    Posts
    1,034
    Post Likes
    Just reread you OP. Bubbling "could" be noncond's as well.Just a thought.

  15. #12
    Join Date
    Mar 2015
    Location
    Hamersville, Ohio
    Posts
    62
    Post Likes
    Mrkelly, it's not "bubbling", ..., it's a swirling trickle, & the pressure rise is ridiculously very small, the low side gauge actually rises slower than what this "trickle" would suggest.

    Coolperfect, the solenoid is approximately 28" away from the middle evaporator.

    Buford, will do, when I go back, & the temp rise across the solenoid is 2.8 degrees.

    This unit is not short cycling.In fact, I called there yesterday, & talked to the "American help", & he said it's running better than ever. (this store has been open only 2 years, after sitting empty 2 years).

    Snapper, it's not, & I'm jus' making observations, & asking questions. My understanding is that these valves are to be "Fully Seated", which it's not doing. If this were a gas valve, it'd be leaking gas into the furnace.I'm analytical in all that I do, whether it be GOD, Family, Country, or my work.

    Now, I'm being told to " that I do not have permission to perform this action, & to refresh the page"! I'm logged in, & down to the bottom right, I can see that I have permission. Waassuupp with that? I'll C & P this & re-post it.

  16. #13
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,578
    Post Likes
    Quote Originally Posted by DavidDeBord View Post

    Snapper, My understanding is that these valves are to be "Fully Seated", which it's not doing. If this were a gas valve, it'd be leaking gas into the furnace
    I think you are seeing refrigerant boiling , because if the valve was indeed leaking by - it would be cycling sir