  1. #27
    Join Date
    Nov 2009
    Location
    USA
    Posts
    26
    This upload interface is a little clunky. Hopefully the troubleshooting guide uploaded. Hope this helps.
    Attached Files Attached Files

  2. #28
    Join Date
    Nov 2009
    Location
    USA
    Posts
    26
    And another one. Is this panel the older one with the numeric codes? Or the clear L display?
    Attached Files Attached Files

  3. #29
    Join Date
    Sep 2005
    Location
    chiller plant
    Posts
    49
    Is this job Mds Pharma ?

  4. #30
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,042
    And another one. Is this panel the older one with the numeric codes? Or the clear L display


    The 80ton RTAA was never manufactured with a numeric code display .
    Is posting confidential service bulletins a good idea Scott ???
    Last edited by Healey Nut; 04-25-2010 at 05:34 PM. Reason: spelling
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  5. #31
    Join Date
    Nov 2009
    Location
    USA
    Posts
    26
    They are "GENERAL" Service not confidential. The RTAA is out of production and I'm sure Trane would like to help wherever possible.

    I usually jump in one time, and post with as good information as possible, and then leave the thread. I don't have much time to visit here. I want all Trane equipment to work properly, so just providing what I can. I did not download those TSB off the Trane Tech side of the site. He could have downloaded them himself.

  6. #32
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,336
    Quote Originally Posted by scott_RWS48 View Post
    And another one. Is this panel the older one with the numeric codes? Or the clear L display?
    looks like a confidential service bulletin to me. trane wants all of their equipment running well. but they will not release any confidential bulletins...most confidential bulletins anymore do not contain a lot of "special-super-secret" info...
    Last edited by jayguy; 04-26-2010 at 07:36 AM. Reason: for the word 'not'...makes a lot of difference!
    "Mother" is the name for God on the lips and hearts of children....The Crow

  7. #33
    Join Date
    Nov 2009
    Location
    USA
    Posts
    26
    LOL...way to go guys, been at Trane a very long time, no need to stick my neck out to help. Don't worry about getting information from this Trane guy anmore. Good job

    I remember trying this forum years ago and ended up in all these side battles. I realized I didn't need to be in the middle of it. After all I don't need to be. Guess what I did the 1st time is what I'll do again. Say good bye

  8. #34
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,336
    Quote Originally Posted by scott_RWS48 View Post
    LOL...way to go guys, been at Trane a very long time, no need to stick my neck out to help. Don't worry about getting information from this Trane guy anmore. Good job

    I remember trying this forum years ago and ended up in all these side battles. I realized I didn't need to be in the middle of it. After all I don't need to be. Guess what I did the 1st time is what I'll do again. Say good bye
    if you want your panties in a wad then fine...the questioning of the confidential service bulletin posting was for your benefit. if you really are a trane technician (still anyway) then you are probably violating the 'never tell any of the super secret info' clauses that you signed.

    i do not care if any service bulletin gets out...i really don't. but i don't post them because i want to keep my job. if you don't or you are not worried then fine...post away.
    "Mother" is the name for God on the lips and hearts of children....The Crow

  9. #35
    Join Date
    Sep 2006
    Posts
    85
    ok my advice check your

    check suction and saturated sensor
    check your connectors on the module
    circuit unit charge
    compressor starts unloaded at around 40 percent should jump up to 60 percent when female is energized
    check expansion valve control response

  10. #36
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,085
    Quote Originally Posted by jayguy View Post
    if you want your panties in a wad then fine...the questioning of the confidential service bulletin posting was for your benefit. if you really are a trane technician (still anyway) then you are probably violating the 'never tell any of the super secret info' clauses that you signed.

    i do not care if any service bulletin gets out...i really don't. but i don't post them because i want to keep my job. if you don't or you are not worried then fine...post away.
    im not a trane employee, however i am always studying trane ioms and i have been to many traing classes as well a teardown schools., i like sb and i wish i could get some more so when i do go out and work on a machine i am prepared., ,. any input

  11. #37
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,085
    Quote Originally Posted by graham View Post
    There aren't vfds on the condenser fans, just fan cycle controls based on head pressure

    Bingo !!!!!!! Houston we have a problem .
    hey graham, can u explain this, if temp is cold outside and there is a call for cooling, i know cond fan will come on for cooling the cond, which would drive head and suction down , i know what a vfd does , and i know what fan cycle does., and if oat sensor set correctly,.
    idk ., what really is goning on, also the fans are already cycling i think.,

  12. #38
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,832
    what part dont you understand???


    Quote Originally Posted by mlkwal1 View Post
    hey graham, can u explain this, if temp is cold outside and there is a call for cooling, i know cond fan will come on for cooling the cond, which would drive head and suction down , i know what a vfd does , and i know what fan cycle does., and if oat sensor set correctly,.
    idk ., what really is goning on, also the fans are already cycling i think.,
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!

  13. #39
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,042
    hey graham, can u explain this

    No head pressure = no suction pressure = no oil movement = no chiller ..Done
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

Page 3 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event