04-18-2010, 07:47 PM #14
There aren't vfds on the condenser fans, just fan cycle controls based on head pressure
Bingo !!!!!!! Houston we have a problem .You bend em" I"ll mend em" !!!!!!!
I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!


-
04-18-2010, 09:42 PM #15
-
04-18-2010, 11:27 PM #16
Professional Member*
- Join Date
- Dec 2008
- Location
- Dixiana, AL
- Posts
- 2,487
-
04-19-2010, 10:21 PM #17
heard of some process machines having to have a 10 minute time delay installed on the load solenoid on these machines to keep from tripping low evap on cold days. no bulletin or factory blessing...just get by
r404a
-
04-19-2010, 11:32 PM #18
Professional Member
- Join Date
- Nov 2005
- Posts
- 1,311
well I went back today, and I took a in depth look at the piping. it is crap! I thought to myself, "who runs chillers in series?" Nobody does! I isolated each chiller independent of each other and ran them one at a time, and no issues. The piping is ran in such a way that you cannot run the chillers in parallel, lame!
These chillers have been in for a few years, could the problem have been that easy?
Thanks for all the help, I still need that service bulletin about the upgraded eprom.I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!
-
04-19-2010, 11:36 PM #19
Professional Member
- Join Date
- Nov 2005
- Posts
- 1,311
is the password for the UCM in the IOM?
I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!
-
04-20-2010, 07:40 AM #20
The eproms have been upgraded, everything after March 2001. There should be VFD's on the fans closest to the control cabinet. Now if they're set up to run is different story. I guess I missed the part about chillers in series. So you've got two chillers in series, pumps on vfd's, no chilled water valves, & chiller condenser fan vfds not set up or working... I just can't possibly see why you'd trip on low evap!
Sic Semper Tyrannis.
-
04-20-2010, 08:31 AM #21
(from RTAA IOM):
Low Evap Rfgt Temp - Ckt 1 or 2 CMR a. The Saturated Evap Rfgt Temp - Circuit 1 or 2 dropped below
the Low Rfgt Temp Cutout Setpoint while the circuit was
running for 30 deg F seconds.
b. See the low ambient ignore time on startup.
Yes, I've gotten this fault before and it turned out to be a fan staging problem. I'll post a thread with information from the RTAA troubleshooting manual titled: RTTA - Variable Speed Fan System
-
04-20-2010, 04:56 PM #22
He doesnt have inverters thats the problem , cant keep the head pressure up in low ambient conditions .
Running the chillers in series is no big deal as long as they are set up correctly ie first in line 58/48 2nd 48/38 could be for a process application .You bend em" I"ll mend em" !!!!!!!
I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!


-
04-21-2010, 07:25 AM #23
I've never worked on an RTAA without fan inverters. I understand this is a factory option. Is it possible to add the inverters in the field? And what all is involved?
-
04-21-2010, 05:27 PM #24
And what all is involved?
Buy em ,mount em , wire em, programme UCM . DoneYou bend em" I"ll mend em" !!!!!!!
I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!


-
04-21-2010, 10:20 PM #25
Professional Member
- Join Date
- Nov 2005
- Posts
- 1,311
who has the passcodes for these machines?
I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!
-
04-21-2010, 11:18 PM #26
Waiting Email Confirmation
- Join Date
- Nov 2009
- Location
- USA
- Posts
- 26
Ok, let’s back up.
++--++ Field start up
--++-- Configuratiuon (be careful, know what you are doing!)
Check very accurately the sub-cooling. RTAA chillers need sub-cooling to be correct at full load as per the IOM.
Another area to check is the load-unload and step loader. Insure NONE of the coils are burned out. Also Insure the output (triac) is working correctly and not shorted. In many cases the coil shorts out and then takes out the output board trac.
Be sure (as another person posted) to check RLA on start up. Normal RLA should be 35-38%. If one or more circuits start and transition (assuming Y-Delta) and immediately show 42-48% OF RLA there is no doubt the PID loop for the EXV will not respond well and tripping off on low evap refrigerant temperature will be a frequent event. The best solution is to install a adjustable LPS and set it to 40 PSI. This will allow the switch to trip, (auto reset) which will flood the evaporator, and on the next start the unit will run fine because plenty of refrigerant will have migrated to the evaporator, allowing time for the EXV to catch up on the next start. This is A LOT cheaper than a new compresser.
Understanding the sequence of operation and knowing what options this chiller has is the key. I suggest you look at these items and post back. 4-degrees superheat and 22 degrees for low refrigerant temp trip.
I’m rather busy these days but if I get a chance to look at this post I’ll try to help you further. RTAA chillers of this vintage usually work well but are very temperamental if anything is not working perfectly well. The algorithms developed for this chiller assume everything is working correctly. As soon as a mechanical, electrical issue arises these chillers become problematic.
Good luck