Thread: RTAA low evap ref. temp. hair falling out!

  1. #21
    Join Date
    Jan 2009
    Location
    Virginia
    Posts
    37
    Post Likes
    Quote Originally Posted by allstar08 View Post
    MN: RTAA0804YN01A3D0BD
    SN: U02M07829
    This thing is driving my nuts. Tied into Summit. Continual low evap ref. temp faults, mostly in the winter months. I have done everything I can think of, from checking the charge to replacing the EEV. Has anyone had this problem?

    I get about one fault a month.
    (from RTAA IOM):
    Low Evap Rfgt Temp - Ckt 1 or 2 CMR a. The Saturated Evap Rfgt Temp - Circuit 1 or 2 dropped below
    the Low Rfgt Temp Cutout Setpoint while the circuit was
    running for 30 deg F seconds.
    b. See the low ambient ignore time on startup.

    Yes, I've gotten this fault before and it turned out to be a fan staging problem. I'll post a thread with information from the RTAA troubleshooting manual titled: RTTA - Variable Speed Fan System

  2. #22
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    He doesnt have inverters thats the problem , cant keep the head pressure up in low ambient conditions .
    Running the chillers in series is no big deal as long as they are set up correctly ie first in line 58/48 2nd 48/38 could be for a process application .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  3. #23
    Join Date
    Jan 2009
    Location
    Virginia
    Posts
    37
    Post Likes
    I've never worked on an RTAA without fan inverters. I understand this is a factory option. Is it possible to add the inverters in the field? And what all is involved?

  4. #24
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    And what all is involved?


    Buy em ,mount em , wire em, programme UCM . Done
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  5. #25
    Join Date
    Nov 2005
    Posts
    1,351
    Post Likes
    Thread Starter
    who has the passcodes for these machines?
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!

  6. #26
    Join Date
    Nov 2009
    Location
    USA
    Posts
    26
    Post Likes
    Ok, let’s back up.

    ++--++ Field start up
    --++-- Configuratiuon (be careful, know what you are doing!)


    Check very accurately the sub-cooling. RTAA chillers need sub-cooling to be correct at full load as per the IOM.

    Another area to check is the load-unload and step loader. Insure NONE of the coils are burned out. Also Insure the output (triac) is working correctly and not shorted. In many cases the coil shorts out and then takes out the output board trac.

    Be sure (as another person posted) to check RLA on start up. Normal RLA should be 35-38%. If one or more circuits start and transition (assuming Y-Delta) and immediately show 42-48% OF RLA there is no doubt the PID loop for the EXV will not respond well and tripping off on low evap refrigerant temperature will be a frequent event. The best solution is to install a adjustable LPS and set it to 40 PSI. This will allow the switch to trip, (auto reset) which will flood the evaporator, and on the next start the unit will run fine because plenty of refrigerant will have migrated to the evaporator, allowing time for the EXV to catch up on the next start. This is A LOT cheaper than a new compresser.

    Understanding the sequence of operation and knowing what options this chiller has is the key. I suggest you look at these items and post back. 4-degrees superheat and 22 degrees for low refrigerant temp trip.

    I’m rather busy these days but if I get a chance to look at this post I’ll try to help you further. RTAA chillers of this vintage usually work well but are very temperamental if anything is not working perfectly well. The algorithms developed for this chiller assume everything is working correctly. As soon as a mechanical, electrical issue arises these chillers become problematic.

    Good luck 

  7. #27
    Join Date
    Nov 2009
    Location
    USA
    Posts
    26
    Post Likes
    This upload interface is a little clunky. Hopefully the troubleshooting guide uploaded. Hope this helps.

  8. #28
    Join Date
    Nov 2009
    Location
    USA
    Posts
    26
    Post Likes
    And another one. Is this panel the older one with the numeric codes? Or the clear L display?

  9. #29
    Join Date
    Sep 2005
    Location
    chiller plant
    Posts
    49
    Post Likes
    Is this job Mds Pharma ?

  10. #30
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    And another one. Is this panel the older one with the numeric codes? Or the clear L display


    The 80ton RTAA was never manufactured with a numeric code display .
    Is posting confidential service bulletins a good idea Scott ???
    Last edited by Healey Nut; 04-25-2010 at 05:34 PM. Reason: spelling
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  11. #31
    Join Date
    Nov 2009
    Location
    USA
    Posts
    26
    Post Likes
    They are "GENERAL" Service not confidential. The RTAA is out of production and I'm sure Trane would like to help wherever possible.

    I usually jump in one time, and post with as good information as possible, and then leave the thread. I don't have much time to visit here. I want all Trane equipment to work properly, so just providing what I can. I did not download those TSB off the Trane Tech side of the site. He could have downloaded them himself.

  12. #32
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by scott_RWS48 View Post
    And another one. Is this panel the older one with the numeric codes? Or the clear L display?
    looks like a confidential service bulletin to me. trane wants all of their equipment running well. but they will not release any confidential bulletins...most confidential bulletins anymore do not contain a lot of "special-super-secret" info...
    Last edited by jayguy; 04-26-2010 at 07:36 AM. Reason: for the word 'not'...makes a lot of difference!
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  13. #33
    Join Date
    Nov 2009
    Location
    USA
    Posts
    26
    Post Likes
    LOL...way to go guys, been at Trane a very long time, no need to stick my neck out to help. Don't worry about getting information from this Trane guy anmore. Good job

    I remember trying this forum years ago and ended up in all these side battles. I realized I didn't need to be in the middle of it. After all I don't need to be. Guess what I did the 1st time is what I'll do again. Say good bye

  14. #34
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by scott_RWS48 View Post
    LOL...way to go guys, been at Trane a very long time, no need to stick my neck out to help. Don't worry about getting information from this Trane guy anmore. Good job

    I remember trying this forum years ago and ended up in all these side battles. I realized I didn't need to be in the middle of it. After all I don't need to be. Guess what I did the 1st time is what I'll do again. Say good bye
    if you want your panties in a wad then fine...the questioning of the confidential service bulletin posting was for your benefit. if you really are a trane technician (still anyway) then you are probably violating the 'never tell any of the super secret info' clauses that you signed.

    i do not care if any service bulletin gets out...i really don't. but i don't post them because i want to keep my job. if you don't or you are not worried then fine...post away.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  15. #35
    Join Date
    Sep 2006
    Posts
    86
    Post Likes
    ok my advice check your

    check suction and saturated sensor
    check your connectors on the module
    circuit unit charge
    compressor starts unloaded at around 40 percent should jump up to 60 percent when female is energized
    check expansion valve control response

  16. #36
    Join Date
    Jan 2009
    Location
    Tampa
    Posts
    1,467
    Post Likes
    Quote Originally Posted by jayguy View Post
    if you want your panties in a wad then fine...the questioning of the confidential service bulletin posting was for your benefit. if you really are a trane technician (still anyway) then you are probably violating the 'never tell any of the super secret info' clauses that you signed.

    i do not care if any service bulletin gets out...i really don't. but i don't post them because i want to keep my job. if you don't or you are not worried then fine...post away.
    im not a trane employee, however i am always studying trane ioms and i have been to many traing classes as well a teardown schools., i like sb and i wish i could get some more so when i do go out and work on a machine i am prepared., ,. any input

  17. #37
    Join Date
    Jan 2009
    Location
    Tampa
    Posts
    1,467
    Post Likes
    Quote Originally Posted by graham View Post
    There aren't vfds on the condenser fans, just fan cycle controls based on head pressure

    Bingo !!!!!!! Houston we have a problem .
    hey graham, can u explain this, if temp is cold outside and there is a call for cooling, i know cond fan will come on for cooling the cond, which would drive head and suction down , i know what a vfd does , and i know what fan cycle does., and if oat sensor set correctly,.
    idk ., what really is goning on, also the fans are already cycling i think.,

  18. #38
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    what part dont you understand???


    Quote Originally Posted by mlkwal1 View Post
    hey graham, can u explain this, if temp is cold outside and there is a call for cooling, i know cond fan will come on for cooling the cond, which would drive head and suction down , i know what a vfd does , and i know what fan cycle does., and if oat sensor set correctly,.
    idk ., what really is goning on, also the fans are already cycling i think.,
    true knowledge exists in knowing that you know nothing.

  19. #39
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    hey graham, can u explain this

    No head pressure = no suction pressure = no oil movement = no chiller ..Done
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  20. #40
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    hey graham!!!!!!!!!!!!!!!!!!!!!!!

    hows it goin??????????????????


    Quote Originally Posted by graham View Post
    hey graham, can u explain this

    No head pressure = no suction pressure = no oil movement = no chiller ..Done
    true knowledge exists in knowing that you know nothing.

+ Reply to Thread
Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •