    hey graham!!!!!!!!!!!!!!!!!!!!!!!

    hows it goin??????????????????


    Quote Originally Posted by graham View Post
    hey graham, can u explain this

    No head pressure = no suction pressure = no oil movement = no chiller ..Done
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!

  2. #41
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,093
    Quote Originally Posted by supertek65 View Post
    what part dont you understand???
    The vfd compared to fan cycle controls on cond fan motors

  3. #42
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,396
    Quote Originally Posted by mlkwal1 View Post
    The vfd compared to fan cycle controls on cond fan motors
    head pressure controls turn the fan on and off based on a single pressure...in this case head pressure.

    the vfd's turn the fans on and off based on the pressure differential between the saturated condensing pressure and the saturated evaporator pressure.

    all txv's (mechanical or electronic) are rated by differential pressure (and a few other things). txv's move their rated tonnage based on this differential pressure. no differential pressure and there isn't any refrigerant movement.

    if the saturated evaporator pressure drops and the saturated condensing pressure stays the same (because the pressure switches only switch based on a single pressure), then the txv tonnage rating goes up and you can move more refrigerant.

    but what happens when the evaporator load goes up? the saturated evaporator pressure goes up, but the saturated condensing pressure stays the same (because of the pressure switches). due to this issue, the tonnage goes down and you can trip due to a heavy load.

    by using the differential pressure, you have several advantages.
    1. maintains txv tonnage at all evaporator loads and condenser loads.
    2. when the saturated evaporator pressure is low AND the outdoor air temp is low (causing the pressure switch to turn OFF some fans), the vfd's would actually turn ON some fans in order to lower the head pressure and gain efficiency (assuming the differential is high enough)
    When the rich wage war, it's the poor who die - Linken Park

  4. #43
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,833
    hey jay
    did you get my email?
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!

  5. #44
    Join Date
    Sep 2008
    Location
    A land down under
    Posts
    309
    Hey mlkwal1,

    Follow the attached link to trane.com literature search and under the helical rotary liquid chillers section download the clear language diaplay troubleshooting bulletin. Page 20-21 details the VSF fan control for the RTAA 70-125 chillers which should help you to understand.


    http://www.trane.com/Commercial/Uplo...-svd03a-en.pdf

  6. #45
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,833
    screwit
    is that your namne or attitude???

    LOL!!!!!!!!!!!!!!!!!!

    or are you a screw chiller guy????

    just wonderin????????????


    Quote Originally Posted by Screwit View Post
    Hey mlkwal1,

    Follow the attached link to trane.com literature search and under the helical rotary liquid chillers section download the clear language diaplay troubleshooting bulletin. Page 20-21 details the VSF fan control for the RTAA 70-125 chillers which should help you to understand.


    http://www.trane.com/Commercial/Uplo...-svd03a-en.pdf
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!

  7. #46
    Join Date
    Sep 2008
    Location
    A land down under
    Posts
    309
    Supertech 65, hope my attitude does not come across that way - it is certainly not intended - been involved predominately with screw chillers for the last 20 years so thought the name was appropriate.

  8. #47
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,833
    LOL!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!

    absolutely not, i am sure you have a great attitude!!!!!!!!!!!!!

    i was just wondering if you had some other reason for the name???

    frank



    Quote Originally Posted by Screwit View Post
    Supertech 65, hope my attitude does not come across that way - it is certainly not intended - been involved predominately with screw chillers for the last 20 years so thought the name was appropriate.
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!

  9. #48
    Join Date
    Sep 2006
    Posts
    85
    Quote Originally Posted by MrSlim View Post
    I've never worked on an RTAA without fan inverters. I understand this is a factory option. Is it possible to add the inverters in the field? And what all is involved?
    yes, this is possible done that on a few units.

  10. #49
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,093
    thanks jay

Page 4 of 4 FirstFirst 1234

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event