Results 1 to 13 of 18
    Nov 2005
    Trane rooftop w/Relia Tel won't C1
    Trane unit cooling only w/ econ.
    MN: TSC092A4R0A0TD
    SN: 253100021L
    has RTOM
    I cannot get 1st stage cooling to fire in test mode and only C2 comes on when the unit goes into cooling. I unplugged J4 on RTRM to eliminate all optional boards, but it still won't fire off in test mode. It doesn't have the LON card. I have verified 24 volts on the LPC return at the board and I can put 24vac to the out put on the board and it will fire, but not at any other time.
    The question is am I missing anything? I am leaning to a new circuit board, but since I don't work on these things everyday I thought you guys might have some advice.
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!
    hey allstar i would try swapping the rtrm board with another unit at location if any that are same. I had a similar problem a couple times one time it was a defective options module figured out by isolating boards. Another was unit had been programed for single stage operation so unit would only turn on one stage even in test mode. best of luck
    Nov 2005
    This unit has worked before, so the programming thing doesn't make sense. Man, I wish there was another board on this roof, the only other unit is an Intelpack.
    Dec 2006
    Middle Tennessee
    Quote Originally Posted by allstar08 View Post
    MN: TSC092A4R0A0TD
    SN: 253100021L
    has RTOM
    when you tested it, was it with the test pins 1 and 2 on the unit itself
    or were you testing your controls
    Jan 2005
    NY
    Might be a dumb question but did you put gauges on this circuit.
    Nov 2005
    Quote Originally Posted by Airmechanical View Post
    I was checking it @ the units test pins
    Nov 2005
    Quote Originally Posted by nytrane View Post
    I checked continuity on all pressure switches, as well as the 24vac input from the LPC on the circuit board.
    Southern California
    allstar,
    Make sure that on the test board you have all the proper jumpers in place....if one is removed it will go into test mode and it will lock a circuit out. i had such problem during a start up of a unit. Check the schematics....if I recall it will tell you where the factory jumper should be. Hope it helps.
    http://i1027.photobucket.com/albums/...g?t=1271631602
    Funny question....Is this unit T-Stat controlled or BMS controlled....If it is BMS controlled(Tracer Summit/Tracker etc.) and has a comm card, disconnect the comm card and isolate the unit. Its very possible someone made a boo boo and disabled circuit 1 through BMS. Regardless of normal operation or Test Mode, a function will not operate if disabled through the configuration menu.
    Nov 2005
    Quote Originally Posted by novato1 View Post
    allstar,
    checked it before the jumper is in place
    Nov 2005
    Quote Originally Posted by lihvac54 View Post
    stand alone, no such luck
    Brooklyn, New York
    Heres an even dumber question. Have u checked ur compressor contactor coil? Sounds like u have an open coil. If that doesnt work, check ur wiring going back to ur economizer board/actuator. U migh have a wire loose, rubbing out, or disconnected.
    Nov 2005
    Quote Originally Posted by brooklyntech View Post
    I can jump 24vac on the circuit board and it will fire.