I would like to know why on some reach in freezers I am getting frost back all the way to the compressor.3 hp system with receiver charged until sight glass has no bubbles. Isn't the TXV supposed to control liquid in the suction line.
-
05-22-2004, 11:31 PM #2
Professional Member
- Join Date
- Aug 2002
- Posts
- 6,047
What's your superheat back at the unit? This temp will tell you whether or not you are getting liquid floodback to your compressor. Or not.
Jus cause the line is icing, doesnt mean it's liquid flooding back.
It's probably just cause it's so cold.
You want thirty degrees, superheat, back at the unit.
-
05-22-2004, 11:46 PM #3
TXV controls superheat.
A Diamond is just a piece of coal, that made good under pressure!
-
05-23-2004, 01:04 AM #4
Professional Member
- Join Date
- Jun 2001
- Location
- San Diego, CA
- Posts
- 1,146
Superheat.
if you want a box at zero degrees, then obviously your coil must be colder - say 10 degrees below zero. Now, if Copeland asks for 20 degrees of superheat at the compressor then that suction temperature needs to be
-10degrees plus 20 or plus 10degrees. That suction line
better frost or we're living on a different planet.
-
05-23-2004, 01:24 AM #5
Regular Guest
- Join Date
- May 2004
- Posts
- 20
The part I don't get is two freezers next to each other at box temp of -10 F both air cooled with 408 gas and one ices up to the compressor and the other doesn't
-
05-23-2004, 02:48 AM #6
I think you need to contact an experienced commercial refrigeration technician for assistance.
-
05-23-2004, 11:19 AM #7
Regular Guest
- Join Date
- May 2004
- Posts
- 20
Thanks for the tip
-
05-23-2004, 11:26 AM #8
I think the freezer with no frost will be burning up a compressor before the one that has some frost.
-
05-23-2004, 12:00 PM #9
Professional Member
- Join Date
- Aug 2002
- Posts
- 6,047
Originally posted by Freezeking2000
I think the freezer with no frost will be burning up a compressor before the one that has some frost.
I agree.
Before I came to this site ... I had a lot of crummy ideas in my head. (DiceMan ... dont even go there!)
Now it all comes together in a kind of harmony. It all makes sense.
And I see others finding the same answers.
There's a lot of "ol wives tales" in our industry about what is right and what is not.
This is a fantastic site!!!
BOSS..... Thanks Again!!!!!!!
-
05-23-2004, 10:37 PM #10If this is what u think, your customers are in a lot of trouble. Do what dave suggests, get an experiended tech for assistance. RSES offers Refergeration 1 & 2 courses. An execellent option for u.Originally posted by crisrs
Isn't the TXV supposed to control liquid in the suction line.If you really know how it works, you have an execellent chance of fixin' er up!
Tomorrow is promised to no one...
-
05-24-2004, 09:15 PM #11
Regular Guest
- Join Date
- May 2004
- Posts
- 245
This reminds me of a conversation I had with an appentice about 15 years ago. We went to service a freezer plant that I worked at regularly. Freezer about 1/2 the size of a football feild. 5 Carrier 5H120's. Box temp -10. He freaked and wanted to adjust all of the tx valves cuz there was ice on the suction service valve.Originally posted by R12rules
Jus cause the line is icing, doesnt mean it's liquid flooding back.
It's probably just cause it's so cold.
Had the same talk about suction temp and superheat at the compressor. If the gas is below freezing tewmp there will be ice. End of story. you need to know the actual temp to determine if there is a problem..
-
05-25-2004, 08:56 AM #12
Some serious education is also needed in the area of DEW point.
If you really know how it works, you have an execellent chance of fixin' er up!