Results 1 to 7 of 7
Thread: dirty sight glass
-
05-22-2004, 08:54 AM #1
Regular Guest
- Join Date
- Apr 2004
- Posts
- 9
working on a walk in pop cooler with an outside condensing unit. The liquid sight glass looks brown and milky; almost looks like mud. The compressor and fan are running, but inside evaporator coil is froze up. Any ideas of what to do?
-
05-22-2004, 10:31 AM #2
Professional Member
- Join Date
- Apr 2002
- Location
- most of the time in the Philippines
- Posts
- 1,206
I think a good start would be thawing out the evap coil, replacing the sight glass and installing a fresh liquid line filter drier. If the compressor is a semi-hermetic, take an oil sample.
-
05-22-2004, 12:07 PM #3
Professional Member
- Join Date
- Aug 2002
- Posts
- 6,047
If the unit is a semi-hernia-metic ..... (I'm gonna patent that name
) you should consider doing the job a favor and change the oil inside the compressor.
But yea, pumpit down, replace those two components; drier and sightglass .... get all ... every speck of ice ...OFF the coils and then see what you got.
-
05-22-2004, 01:26 PM #4
First, find out why the cooler is down. It's not down because of a dirty old sightglass.
-
05-22-2004, 03:50 PM #5
Professional Member
- Join Date
- Aug 2002
- Posts
- 6,047
The coil's iced. That means the dew point of his liquid refreshment went down to sub atomic level. And so ....it's obvious he has a system which is low on charge.Originally posted by condenseddave
First, find out why the cooler is down. It's not down because of a dirty old sightglass.
Or ... someone partially blocked his doomi-hichey...
-
05-22-2004, 06:32 PM #6
Professional Member
- Join Date
- Oct 2003
- Location
- new orleans,la
- Posts
- 147
That cooler must had refrigerant leak somewhere on low side to the point that too much water is shown up in the sighglass.
One quick way to find out is testing the cutout of low pressure control and see if it's cut out below O lb, vacuum will suck in moisture through the leak spot , next find the leaks and correct it....then new drier, sighglass and fresh gases.
I like the ideas of oil change on(poly ester)but sometime second drier also work next couple day if you have to.koolrite837
-
05-25-2004, 08:40 AM #7
Professional Member
- Join Date
- Jun 2003
- Posts
- 118
Did someone add leak checking dye to the oil? That will make the compressor sight glass look like there is mud in the oil. This can carry over to the liquid line if your compressor is pushing oil. It does sound like you have a problem. I would do the things guys are reccomending here, quickly! Roger
If you don't have the time to do it right the first time, when will you have the time to do it over?


Reply With Quote