    My book (2003)doesn't show an FA048 as an approved match,just the 060.What do you have?

  2. #28
    Join Date
    Apr 2004
    Location
    Midwest
    Posts
    2,683
    Originally posted by dash
    hvac r,

    My book (2003)doesn't show an FA048 as an approved match,just the 060.What do you have?
    Oh boy, how did I know you were not going to miss that Dash? LOL

    I wasn't going to open a whole can of worms here as unapproved matches happen all the time (again not a good choice) but since you pointed it out, here we go...

    A 38EYG048 is not an approved match with the FA048. This is due to the coil circuit flow not being enough with Puron as opposed to R-22. You need a larger surface area. This can become a greater problem in the heating mode.

    You can locate the facts in the Product Data for the 38EYG, page 29, 2004 catalog, form# 38EYG-3PD.

    Not sure about in the Dallas area, but I would think a Carrier dealer or distributor could get you a copy of this.

    Good Luck
    Live each day like it is your last, for one day you will be right!

  3. #29
    Join Date
    Sep 2003
    Posts
    47
    Thanks for the info guys, you always seem to impress me.

    Ok, here's an update. I called the dealer here on Friday, and he said that they DID replace the metering device, and add the TXV. He's going to send someone over next week to take another look at the system.

    When you say it's "not an approved match", you are saying from Carrier itself, right? Could this be the cause of my humidity problem? If so, I may be able to request he change the air handler for me.
    Here's the situation: the home we bought is in a brand new subdivision of 420+ homes when it is completed. There are 2 builders, splitting the homes. The same HVAC company is doing ALL the heating/cooling for the builder I used. The builder is a no-nonsense guy, and if they shouldn't be putting these systems together like this, I'd bet he'll put pressure on the HVAC company to set things right. Considering the $$$ involved, I'd bet it would be taken care of quick.


  4. #30
    Check out http://www.centralcityair.com look in the library on undersizing coils. Contact them if you have to (out of Houston)

  5. #31
    you will NEVER NEVER NEVER did i say NEVER be happy with a heat pump where you are in that set up...look at the heat pump coil specs...twice the surface area and square ft of a slab coil of the same ton...you bought a heater that cools not a cooler that heats...it is over ..buy a thermastor central dehumidifier...to say a heat pump cools just as good as a non heat pump?...well i am waiting to see it...havent yet in 35 years...but!!

  6. #32
    Join Date
    Sep 2003
    Posts
    47
    Well Airman, I didn't have much choice, since this development does not have gas.

  7. #33
    sorry not trying to rub it in just stating the facts as i see it...you will probably be better of changing the cooling coil to a smaller one and dont use a heat punp to heat..

  8. #34
    Join Date
    Apr 2005
    Location
    Kingston Ontario Canada
    Posts
    1,221
    Originally posted by topdog
    The board for blower operation is inside this unit and it is a VS. Make sure board is set up properly.As Short Circuit and justwarmingup has already posted.You will see better results,probably wasn't done and left at factory default. Puron??? Not so sure if it is a VS motor in the air handler maybe dash or hvac r us 2 or jrbenny will come in. They'll know.

    [Edited by topdog on 05-19-2004 at 09:41 PM]
    I don't think it's a variable speed motor in air handler g]either. Carrier's variable's have a V in the model # I believe.

    Thorton

  9. #35
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    Even if everything about the equipment was perfect, wich is sounds like it is not, you will have high humidity with a single stage system with the kind of weather we have been having for the last few weeks here in the DFW area.

    Systems are generally sized in this area to keep it 75º with 50% RH inside the house with 100º oudoor temperature and ~25 grains difference of moisture.

    Even if it isn't oversized at all, it is big enough that it won't run enough in this 70-78º humid weather to keep the humidity levels down.
    If more government is the answer, then it's a really stupid question.

  10. #36
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    6,592
    Originally posted by shepx2
    Well Airman, I didn't have much choice, since this development does not have gas.
    With moisture from the occupants, normal air & moisture infiltration, up to 100 pints/day of moisture must be removed during 60-70^F outdoor dewpoints. The simplest fix is adding a 100 pint/day dehumidifier to the air handler. The dehumidifier will remove enough moisture to provide 50%RH even without any a/c load or operation. Using a high efficiency unit like the Ultra-Aire 100V and being able to set the t-stat higher keeps the operating cost inline with the a/c only. I maintain that the ideal sized a/c is unable to maintain <50%RH during the 65^F-75^F "rainy spell" of weather without supplemental dehumidification. I will supply a set of inside/outside data loggers to prove over cooling is not a practical solution to this problem. Removing 100 pints of moisture per day to maintain <50%RH by overcooling requires 1.5 ton of constant a/c. This will not be a comfortable home. The home is a flywheel and the lenght of the wet/cool weather is load. Without supplemental dehumidification, over-dry the home during hot weather, avoid fresh air ventilation, and lengthly wet, cool weather.

  11. #37
    Join Date
    Jun 2004
    Location
    4H: Hot, Humid Houston H.O.
    Posts
    3,304

    Your options

    Teddy Bear tends to advocate getting a Thermastor dehumidifier system and I tend to agree with him. Airman has really studied what it takes to dehumidify using the AC system and if he says you are way out of whack, I would believe him.

    I bought a floor-standing Thermastor model and have observed about a 10 point drop in relative humidity using it, near Houston TX. If you want to "test" the idea by buying a cheaper dehumidifier and running it first, you can do that for a couple hundred dollars -- with reduced capacity and you will soon tire of manually emptying a water bucket<g>.

    Your Dallas location will soon get into cooling season and you *might* see things getting better. But your Mississippi reading of 52% indoor RH is awfully good, I would not expect your new house to do anything like that.

    By all means, if you have ducts in the attic and a supply leak, the result will be negative indoor pressure and outside hot humid air will be pulled in. If this turns out to be the case, fixing the leaks will tend to solve your problem. It will cost a few bucks to investigate but in my opinion will be money well invested.

    Best of luck -- P.Student

  12. #38
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,379

    Frown

    Originally posted by shepx2
    Ok, I got up in the attic. The model of the Air Handler is FA4BNF048.
    FA is a CONSTANT Speed.
    Plus, 4-ton unit seems to be a bit oversized for 1,900 Sq. Feet.

    You may wish to investigate the use of AprilAire model 1700 or Therma-Stor UA_135H dehumidifiers.
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event