Results 1 to 10 of 10
Thread: Singer refigeration unit.
-
05-19-2004, 01:13 AM #1
I have an old Singer refigeration unit 10ton, with
a coupland hermetic compressor, that is testing
me. It is a 1976 unit, but compressor was replaced
with a remanufactured unit in 1999.
This unit runs on freon 409a, and is a high temp
unit 38 degrees.
The problem I am having is low high side pressure
160psi, and very low low side 18" vacuum.
The unit has no leaks, and is properly charged.
I evacuated unit, and leak checked, all ok.
Filter dryers are ok also, and valves all
checked good. At these pressures, unit is only
producing about 20%. At this building there are
3 other Singer units 2 20 ton units, and another
10 ton unit. I have replaced compressors in 2
of the other 3 in the last 2 years, and no
problems.
The only item I have not checked is the expansion
valve, because it is 25' up on a ceiling in a large
cold vault surrounded by merchandise. But at
these preasures I do not feel valve is stuck.
Any ideas???
Edward
-
05-19-2004, 01:28 AM #2Why not? L.L.S good?Originally posted by edward301
But at
these preasures I do not feel valve is stuck.
-
05-19-2004, 04:54 PM #3
Is this sytem actually allowed to run at these conditions???? I should hope not or you'll be replacing another compressor real soon.
No refrigerant is moving here. You have a major restriction of refrigerant flow. Trace it out......filter-drier, liquid line solenoid, TXV screen, TXV powerhead, stuck TXV.......
Your going to have to get to the evap and the TXV one way or the other to fix this. Get the customer (or whoever) to break you a path and clear the area so you can work.
-
05-19-2004, 06:57 PM #4
Regular Guest
- Join Date
- Jan 2002
- Posts
- 1,895
You could try some animal sacrifice or a witch docter but if the coil hasn't been looked at common sence says there is where the problem probably is.
-
05-19-2004, 07:11 PM #5
Regular Guest
- Join Date
- Mar 2004
- Location
- Windsor, ON Canada
- Posts
- 168
If there is no lls, try adding a little refrigerant, if head goes up a little and suction continues in a vacuum, txv is stuck...guaranteed.
-
05-19-2004, 07:14 PM #6
Singer refigeration unit fixed.
Gained access to the evaporator unit 25' up, and found the
problem. Whoever replaced the evaporator 5 years ago
did not wire the unit in properly. An electric valve was
intermittant, shutting off the flow of freon at random
times. Rewired unit, now everything perfect. Cold as
can be.
Edward.
-
05-19-2004, 09:29 PM #7
Re: Singer refigeration unit fixed.
Hmmmm, for 5 years ran great and now this shows up? Smoething's fishy in Gotham, Batman.Originally posted by edward301
Whoever replaced the evaporator 5 years ago
did not wire the unit in properly......Rewired unit, now everything perfect.
-
05-19-2004, 09:30 PM #8
Professional Member
- Join Date
- Aug 2002
- Posts
- 6,047
WAY TA GO Edward!!!
And welcome to the forum community.
(watch out for DiceMan ... he attempts to intimidate newcomers)
Seriously ....
-
02-12-2008, 06:58 PM #9
Regular Guest
- Join Date
- Apr 2005
- Location
- dallas texas
- Posts
- 21
AN Electric Valve?
DO you mean the Pump Down Solenoid? Also if you Low pressure Cut out is set right it would not run In an 18 inch vacuum
-
02-12-2008, 10:00 PM #10
Wow, this post is so old I barely remember it. Those units are still running,
doing quite well. One 20 ton unit did give me problems last fall, turned out
the head pressure control valve had gone bad.
New valve, doing good.
I am adding a new 30 ton refigeration unit, except the freight company
damaged the evaporator. They hit and badly bent the suction line
exiting the evap cabinet, which in turn bent the copper line all the way
up the evap coil.
New evap on order, freight company bought the old one.


Reply With Quote