    I've got a Kolpak walk in freezer that has a few, 5 to 10, icicles forming at the inlet air intake starting about 4 to 6 inches up from the wire grill on the condensing unit side of the housing and forming down a few inches below the grill.. I have sealed every opening, electrical, evap. housing cover, etc. The only area not air sealed is the drain line from the pan out to the condensate pan.
    The unit has VERY LITTLE coil frost build up and the entrance into this box is through another walk in cooler.
    We were getting build up around the evap fan shroud, but the additional sealing has appeared to take care of that.
    The entire "unit" gasket looks like its okay. That's the only other guess I have where air is coming in at.
    Thanks.

  2. #2
    Join Date
    Apr 2002
    Location
    most of the time in the Philippines
    Posts
    1,211
    1. Check the defrost termination/fan delay sequence. Could be the defrost cycles are too long or the evaporator fans are being delayed until the coil is cold or both.

    2. The drain line is trapped outside the box, right?

    3. Install a door switch that shuts off the refrigeration and the evaporator fans when the door is opened.