Thread: trane cvhe

  1. #1

    trane cvhe

    I am currently having issues with a trane cvhe centrifugal. On start-up sequence I cannot get any voltage coming through the K1,2,3 contacts on number 8 & 9 (1tb2 terminal strip). Then the unit goes into alarm. (momentary loss in power). To me it looks like there is a problem with the board (1u2). Anybody with any experience with this problem?

  2. #2
    Join Date
    May 2006
    Location
    N.E. IA
    Posts
    512
    Quote Originally Posted by Max77 View Post
    I am currently having issues with a trane cvhe centrifugal. On start-up sequence I cannot get any voltage coming through the K1,2,3 contacts on number 8 & 9 (1tb2 terminal strip). Then the unit goes into alarm. (momentary loss in power). To me it looks like there is a problem with the board (1u2). Anybody with any experience with this problem?
    Please post model and serial numbers. That will tell us which vintage controls you have. (Unless someone retrofitted newer controls on an older machine).
    "Wheel" mechanics work on "Wheel" chillers

  3. #3
    If this is a black classic 8&9 is your evap flow switch.

  4. #4
    Join Date
    Jan 2010
    Location
    In a Pineapple Under the Sea
    Posts
    149
    I'm going to go way out on a limb and guess its either a UCP1 or 2

    You need 2 Trane manuals, CVHE-SB-22A & CVHE-SB-32A each is the troubleshooting manual for each chiller control system.

  5. #5
    Join Date
    Jun 2009
    Location
    Florida
    Posts
    540
    Quote Originally Posted by Doesn'tPhaseMe View Post
    I'm going to go way out on a limb and guess its either a UCP1 or 2

    You need 2 Trane manuals, CVHE-SB-22A & CVHE-SB-32A each is the troubleshooting manual for each chiller control system.
    I'm guessing UCP1. Check your starter auxilliary switches.
    Low Pressure Forever!

    If you know heavy metal, you can work anywhere-Dave Andreson

    Anchors Aweigh my boys, Anchors Aweigh!
    Farewell to foreign shores, We sail at break of day. Through our last night on shore, Drink to the foam. Until we meet once more. Here's wishing you a happy voyage home!

  6. #6
    Join Date
    Oct 2006
    Location
    Central Texas
    Posts
    633
    695 panel, a black panel dosen't see momentary power loss. Check your F2 fuse, if you've got no power on the points you listed. As stated above use the CVHE-SB-22a to help you out.
    Sic Semper Tyrannis.

  7. #7
    Join Date
    Oct 2006
    Location
    FL
    Posts
    75

    CVHE-SB-22A wanted

    Please email me CVHE-SB-22A.
    Thanks

  8. #8
    hope i do this right.Hope this goes through
    Attached Files Attached Files

  9. #9
    Join Date
    Oct 2006
    Location
    FL
    Posts
    75
    Quote Originally Posted by allchlrstech View Post
    hope i do this right.Hope this goes through
    Thank you so much.

  10. #10
    Join Date
    Aug 2008
    Location
    Parts Unknown
    Posts
    81

    Cool UCP 1 and 2 Trouble Shooting Manual

    I know this post is from a couple of months ago but I am in need of UCP 1 and 2 trouble shooting manual. Dose anyone know the part number for the teardown and service lit for the latest CVHE and CVHF chillers. I have the 400 page one from the late 80's but I amlooking for the latest and greatest.
    Last edited by megohm; 06-25-2010 at 10:04 PM. Reason: Entered wrong value

  11. #11
    Join Date
    Oct 2004
    Location
    Metro ATL
    Posts
    454
    Quote Originally Posted by txhvac View Post
    695 panel, a black panel dosen't see momentary power loss. Check your F2 fuse, if you've got no power on the points you listed. As stated above use the CVHE-SB-22a to help you out.
    Not to get picky but the black classic does see momentary loss of power. It's called a distribution fault.

  12. #12
    Quote Originally Posted by megohm View Post
    I know this post is from a couple of months ago but I am in need of UCP 1 and 2 trouble shooting manual. Dose anyone know the part number for the teardown and service lit for the latest CVHE and CVHF chillers. I have the 400 page one from the late 80's but I amlooking for the latest and greatest.
    The cvhesb22a I posted earlier is ucp1, This cvhesb32 I am posting now is ucp2.You can sighn up for Trane comforsight to get the latest and greatest,
    You have to be a Trane Dealer I think to get access to comfortsight and it cost you a yearly fee.It suppost to replace the Trane Eagle disk collection, that you had to pay to get a new disk 1 every year.
    Attached Files Attached Files

  13. #13
    Join Date
    Aug 2008
    Location
    Parts Unknown
    Posts
    81

    UCP 1 and 2 Trouble Shooting Manual

    Thanks for the info. I would love to sighn up for the comfort site but being considered the competition they will not let me so if you need any information or help I am here to help as well.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event