    Jan 2005
    steeler nation
    comfort view and t59 stat
    i have a building with 3V, comfortview and t59 thermostats with setpoint adjust.
    if using the thermostat setpoint do i need to do anything special with the occ/unocc setpoints in comfortview ?
    i was told that the heat/cool setpoints may have to be set the same such as 72/72.
    IV IV IX
    use your head for something other than a hat rack.......Gerry
    We have freedom because somebody fought for it.
    We keep it because we are willing to fight for it.
    We lose it because we are not willing to fight for it.
    Dec 2006
    Washington, DC
    Do you have the ones with the slide at the bottom or the up/down arrow buttons? No difference in operation except with the button style you cant change the offset number on the display to match SET_LIMT, it is always +/- 2 on the display.
    You need to enable this function in the SERVICE\OPTIONS\SET_LIMT table. The default is 2.0, which is enabled & adjusts up or down 2dF. A value of 0.0 will disable offset. The offset only effects occupied setpoints.
    I typically set the occupied setpoints at 72/74 with a 2.0 offset. This gives a range of 70/72 to 74/76. I find 2dF between them works well for most jobs. I never match the OccLow & OccHigh or go closer than 1dF, this gives you a 1dF Vent mode.
    Quote Originally Posted by Qui-Gon Jinn (Star Wars Episode 1)
    "The ablilty to speak does not make you intelligent!"
    Jan 2005
    steeler nation
    thanks for the help. i'm a newbie when it comes to the carrier stuff.
    these stats have the buttons.
    IV IV IX