    Anyone have experience with this refrigerant? Will i have to change expansion valve when converting from r-12? This is a low temp. box that someone else has put 414 in and she won't pull down below 15deg. Seems like there is no way to use sight glass. When bubbles clear it is overcharged.Is there a better choice for refirgerants to convert from r-12?

  2. #2
    Join Date
    Jan 2003
    Location
    Olathe Kansas
    Posts
    246
    Post Likes
    Could be that you may have other problems. I use 414 in all the old R-12 systems. No problems yet.Some of them been going 4 years now. Give us more info.

  3. #3
    Join Date
    Dec 2003
    Location
    Salisbury, MD.
    Posts
    1,504
    Post Likes
    Thread Starter
    i haven't gotten into the system yet. it is a new customer that has had someone else working on it. they replaced a suction drier because it had been left on there so long it rusted out. the condensing unit is outside and i had between 25 and 30lb. suction, 180lb. head. When i cleared the sight glass it flooded back. the last guy attached the liquid line to the suction line as a heat exchanger. the pressures seem highe than r-12 so i was wondering if the expansion valve was compatible. the unit is dirty, has leaks, and very poor brazing. my question is should i keep the same txv while i repair the other problems? I have seen a lot of people use mp39 that caused a lot of the old r-12 systems to lose compressors because of excesive head pressure. is the 414 the best replacement for the 12?

  4. #4
    Join Date
    Nov 2003
    Posts
    504
    Post Likes
    I use Hot Shot all the time as a 12 replacement. You don't have to change the TXV. You got a good handle on it...don't clear the sightglass, etc.

    Just make sure you charge with the bottle upright. It's different than the rest of the blends. I've caught myself doing that a couple times. My mind says "turn it upside down," but then I realize that isn't correct.

  5. #5
    Join Date
    Dec 2007
    Posts
    1
    Post Likes

    Arrow 414 Replacement

    I feel like I am beating a Dead Horse - I keep telling you guys MAXIFRIG does much better - Much colder, they say its something to do w/ the head pressure - With our coolers my amateur nephew puts it my low temp units and in 3 years everything perfect w/ no comp failures - NEGITIVES = It is only available direct from them and they are difficult to get along with = BUT, Hey no price increases so far and it works terrific so we get 22 & 502 also - Good Luck Guys ............

  6. #6
    Join Date
    May 2004
    Posts
    2,622
    Post Likes
    Quote Originally Posted by dorrmann View Post
    I use Hot Shot all the time as a 12 replacement. You don't have to change the TXV. You got a good handle on it...don't clear the sightglass, etc.

    Just make sure you charge with the bottle upright. It's different than the rest of the blends. I've caught myself doing that a couple times. My mind says "turn it upside down," but then I realize that isn't correct.
    All the jugs of hotshot I have bought have to be turned upside down. Better to read the jug than do it wrong.

  7. #7
    Join Date
    Jan 2006
    Location
    In a land far, far away
    Posts
    19,523
    Post Likes
    This is a low temp. box that someone else has put 414 in and she won't pull down below 15deg.
    That's typical for a low temp system with 414b. Hot Snot will do a decent job for medium temp but is terrible for low temp. The ONLY good alternative for a low temp R-12 system is MP-66.

    And forget about the "don't fill the site glass crap", it the site glass isn't full you're not getting a full column of liquid to the TXV....period! Anyone that tells you any different either dunno what they're talking about or they work for ICOR.

  8. #8
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    6,125
    Post Likes
    Agreed with K-fridge. There is NOT an expansiion valve on the market yet that works well not having a full column of liquid to it. PERIOD!!!!
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

  9. #9
    Join Date
    Jan 2006
    Location
    In a land far, far away
    Posts
    19,523
    Post Likes
    But you can probably use the same TXV if it was the correct one to begin with. After you fill the site glass (subtle hint) and get the box close to temp, check the SH and adjust as needed. It's fairly common when switching to blends that the TXV will need closed a bit.

    You should be running at least 1/2 AB oil in the compressor with MP-66 unless it's a close coupled system.

  10. #10
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Post Likes
    Quote Originally Posted by k_fridge View Post
    And forget about the "don't fill the site glass crap", it the site glass isn't full you're not getting a full column of liquid to the TXV....period! Anyone that tells you any different either dunno what they're talking about or they work for ICOR.
    This just keeps coming up - donit

    A guy should make a YES THE LL SIGHT GLASS NEEDS TO BE CLEAR sticky thread

  11. #11
    Join Date
    Dec 2007
    Location
    Indianapolis
    Posts
    677
    Post Likes
    Quote Originally Posted by markettech View Post
    This just keeps coming up - donit

    A guy should make a YES THE LL SIGHT GLASS NEEDS TO BE CLEAR sticky thread
    Ya tryin' to put the rest of us out of a job when the others muck up?

    B-

  12. #12
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Post Likes
    Quote Originally Posted by Biblepoet View Post
    Ya tryin' to put the rest of us out of a job when the others muck up?

    B-

  13. #13
    Join Date
    Jan 2006
    Location
    In a land far, far away
    Posts
    19,523
    Post Likes
    Quote Originally Posted by markettech View Post
    This just keeps coming up - donit

    A guy should make a YES THE LL SIGHT GLASS NEEDS TO BE CLEAR sticky thread
    It absolutely amazes me that so many people believe this junk. And people wonder why I have issue with a certain refrigerant manufacturer.

  14. #14
    Join Date
    Apr 2005
    Location
    dallas texas
    Posts
    21
    Post Likes

    414

    I have not had any problem with 414 On some of the older systems you cant clear the sight glass I just charge the system by amp draw on the Compressor but make sure the box is warm when you start and charge until you get TO RLA rating on compressor then watch the temp

  15. #15
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,520
    Post Likes
    Just dump some HP-80 in it clear sight glass and be done with it no txv
    change either.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  16. #16
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,520
    Post Likes
    And on more thing K, MT,POWEL ICE,LUCKSTER can anyone show me where
    one manufacturer recomends hot sh** for anything.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  17. #17
    Join Date
    Aug 2007
    Location
    Chicagoland Area
    Posts
    43
    Post Likes
    MP66 is for low temp swap Mp39 is a med temp swap. HP 81 is for ice machines for R12 swap. Copeland will not warrant any compressor if they find out 414 has been used in it. Has anyone used the 416 yet? I have a friend that his boss swears by it for med and high temp 12 systems. I am the service manager for a mechanical co. that does only resturant work. My guys have a basic supply of refrigerants on thier trucks MP39, R22, 404A,134A, and 408A for the 502 systems, we do have the other mixes at the shop for those units that have been worked on prior to us being there. The refrigerant market is getting so complicated that you need a chemistry degree to work on these units. Then you have Joe Blow resturant owner that got a good deal on a German made unit with 507 in it. Makes a person wonder why do I hate myself so much.
    Last edited by tazzman1945; 01-01-2008 at 09:43 PM. Reason: spelling

  18. #18
    Join Date
    Jun 2005
    Location
    Atlanta - Retired
    Posts
    1,250
    Post Likes
    First let’s verify the application of the refrigerants we're discussing.

    R-12 Replacements
    R401A -- MP39: -10 or higher SST
    R401B -- MP66: +25 and lower SST
    R414B -- Hot Shot

    R-502 Replacements
    R408A
    R402A -- HP80
    R402B -- HP81 Similar components to R-402A but contains more R-22 and less R-125. This lowers the discharge pressure closer to R-502, however the discharge temperature increases compared to R-502. This is a benefit in ice machines, where the blend is primarily used, because it improves harvest times.

    Copeland does not list R414B -- Hot Shot as an approved refrigerant. Follow this link for approved refrigerants. View section 26, 93-11R14 bulletin.

    http://www.hvacrinfo.com/ae_index.htm

    Also, here is the statement made by Copeland concerning its chart:

    "Copeland Engineering has recently updated its Accepted Refrigerant/Lubricants chart. The refrigerants and lubricants on this chart have been tested and approved by Copeland Engineering. Using refrigerants and lubricants not tested and approved by Copeland may result in voiding the warranty".

    I'm not condemning Hot Shot, it works fine in some applications.

    P.S. Fill the sight glass.

    Powell
    Last edited by powell; 01-02-2008 at 08:40 AM.

  19. #19
    Join Date
    Feb 2004
    Location
    Medford Oregon
    Posts
    807
    Post Likes
    MAXIFRIG is a Hyrocarbon, it is dangerous and not approved by anyone and hydrocarbons are illegal per EPA
    best LT R12 replacement is MP-66

  20. #20
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,520
    Post Likes
    Thank's powell.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

+ Reply to Thread
Page 1 of 4 1234 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •