Thread: r-414

  1. #1
    Join Date
    Dec 2003
    Location
    Salisbury, MD.
    Posts
    1,480
    Anyone have experience with this refrigerant? Will i have to change expansion valve when converting from r-12? This is a low temp. box that someone else has put 414 in and she won't pull down below 15deg. Seems like there is no way to use sight glass. When bubbles clear it is overcharged.Is there a better choice for refirgerants to convert from r-12?

  2. #2
    Join Date
    Jan 2003
    Location
    Olathe Kansas
    Posts
    246
    Could be that you may have other problems. I use 414 in all the old R-12 systems. No problems yet.Some of them been going 4 years now. Give us more info.

  3. #3
    Join Date
    Dec 2003
    Location
    Salisbury, MD.
    Posts
    1,480
    i haven't gotten into the system yet. it is a new customer that has had someone else working on it. they replaced a suction drier because it had been left on there so long it rusted out. the condensing unit is outside and i had between 25 and 30lb. suction, 180lb. head. When i cleared the sight glass it flooded back. the last guy attached the liquid line to the suction line as a heat exchanger. the pressures seem highe than r-12 so i was wondering if the expansion valve was compatible. the unit is dirty, has leaks, and very poor brazing. my question is should i keep the same txv while i repair the other problems? I have seen a lot of people use mp39 that caused a lot of the old r-12 systems to lose compressors because of excesive head pressure. is the 414 the best replacement for the 12?

  4. #4
    Join Date
    Nov 2003
    Posts
    501
    I use Hot Shot all the time as a 12 replacement. You don't have to change the TXV. You got a good handle on it...don't clear the sightglass, etc.

    Just make sure you charge with the bottle upright. It's different than the rest of the blends. I've caught myself doing that a couple times. My mind says "turn it upside down," but then I realize that isn't correct.

  5. #5

    Arrow 414 Replacement

    I feel like I am beating a Dead Horse - I keep telling you guys MAXIFRIG does much better - Much colder, they say its something to do w/ the head pressure - With our coolers my amateur nephew puts it my low temp units and in 3 years everything perfect w/ no comp failures - NEGITIVES = It is only available direct from them and they are difficult to get along with = BUT, Hey no price increases so far and it works terrific so we get 22 & 502 also - Good Luck Guys ............

  6. #6
    Join Date
    May 2004
    Posts
    1,865
    Quote Originally Posted by dorrmann View Post
    I use Hot Shot all the time as a 12 replacement. You don't have to change the TXV. You got a good handle on it...don't clear the sightglass, etc.

    Just make sure you charge with the bottle upright. It's different than the rest of the blends. I've caught myself doing that a couple times. My mind says "turn it upside down," but then I realize that isn't correct.
    All the jugs of hotshot I have bought have to be turned upside down. Better to read the jug than do it wrong.

  7. #7
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    14,539
    This is a low temp. box that someone else has put 414 in and she won't pull down below 15deg.
    That's typical for a low temp system with 414b. Hot Snot will do a decent job for medium temp but is terrible for low temp. The ONLY good alternative for a low temp R-12 system is MP-66.

    And forget about the "don't fill the site glass crap", it the site glass isn't full you're not getting a full column of liquid to the TXV....period! Anyone that tells you any different either dunno what they're talking about or they work for ICOR.

  8. #8
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    6,006
    Agreed with K-fridge. There is NOT an expansiion valve on the market yet that works well not having a full column of liquid to it. PERIOD!!!!
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

  9. #9
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    14,539
    But you can probably use the same TXV if it was the correct one to begin with. After you fill the site glass (subtle hint) and get the box close to temp, check the SH and adjust as needed. It's fairly common when switching to blends that the TXV will need closed a bit.

    You should be running at least 1/2 AB oil in the compressor with MP-66 unless it's a close coupled system.

  10. #10
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Quote Originally Posted by k_fridge View Post
    And forget about the "don't fill the site glass crap", it the site glass isn't full you're not getting a full column of liquid to the TXV....period! Anyone that tells you any different either dunno what they're talking about or they work for ICOR.
    This just keeps coming up - donit

    A guy should make a YES THE LL SIGHT GLASS NEEDS TO BE CLEAR sticky thread

  11. #11
    Join Date
    Dec 2007
    Location
    Indianapolis
    Posts
    677
    Quote Originally Posted by markettech View Post
    This just keeps coming up - donit

    A guy should make a YES THE LL SIGHT GLASS NEEDS TO BE CLEAR sticky thread
    Ya tryin' to put the rest of us out of a job when the others muck up?

    B-

  12. #12
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Quote Originally Posted by Biblepoet View Post
    Ya tryin' to put the rest of us out of a job when the others muck up?

    B-

  13. #13
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    14,539
    Quote Originally Posted by markettech View Post
    This just keeps coming up - donit

    A guy should make a YES THE LL SIGHT GLASS NEEDS TO BE CLEAR sticky thread
    It absolutely amazes me that so many people believe this junk. And people wonder why I have issue with a certain refrigerant manufacturer.

Page 1 of 6 123456 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event