Causes of Negative Subcooling
First of all, is it possible to have negative subcooling (ie liquid line temp is greater than temp of condensation)? Second, what could cause this to happen?
-
This happens whenever the compressor absorbs heat instead of rejecting it ! Many causes ! Read the book ..
"Rock-n-Roll " Ain't noise pollution..

-
 Originally Posted by INTECHBILL
This happens whenever the compressor absorbs heat instead of rejecting it ! Many causes ! Read the book ..
The compressor doesn't reject heat. It just moves vapor.
The condenser coil rejects heat. 
OP. Check your gauges and temp meter.
-
 Originally Posted by beenthere
The compressor doesn't reject heat. It just moves vapor.
The condenser coil rejects heat.
OP. Check your gauges and temp meter.
expl # 1
If I'm not mistaken if the compressor is loaded with oil , the oil will hold heat and there you have it yes?
Expl #2
If the outdoor coil is restricted the compressor will overheat - yes ?
Expl # 3
many of my medium and Low temp application compressors move some liquid for proper S/c / S/h - yes ?
NEXT !
"Rock-n-Roll " Ain't noise pollution..

-
 Originally Posted by INTECHBILL
expl # 1
If I'm not mistaken if the compressor is loaded with oil , the oil will hold heat and there you have it yes?
Expl #2
If the outdoor coil is restricted the compressor will overheat - yes ?
Expl # 3
many of my medium and Low temp application compressors move some liquid for proper S/c / S/h - yes ?
NEXT !
HUH?
If the compressor is loaded with oil, you got a problem. FIX IT!
If the outdoor coil is restricted, you got a problem. FIX IT!
In NO application should liquid return to the compressor. NONE! Liquid is hard on pumps.
BT is right. The compressor neither absorbs nor rejects heat, only moves vapor.
Maybe you ought to
-
 Originally Posted by jpsmith1cm
HUH?
If the compressor is loaded with oil, you got a problem. FIX IT!
If the outdoor coil is restricted, you got a problem. FIX IT!
In NO application should liquid return to the compressor. NONE! Liquid is hard on pumps.
BT is right. The compressor neither absorbs nor rejects heat, only moves vapor.
Maybe you ought to 
Have you not worked on Semi-Hermetic Low Temp Commercial applications -- If the compressor creates heat by "heat of compression" and can't get rid of the heat -- then what happens ! OHHH ! Just the other day a contractor called me to an ice cream plant & the compressor was operating under normal conditions pumping a liitle liquid .. & Of course I understand the basic principles of refrigeration -- you probably have worked on some equipment that was designed by yours truly !!
"Rock-n-Roll " Ain't noise pollution..

-
 Originally Posted by INTECHBILL
This happens whenever the compressor absorbs heat instead of rejecting it ! Many causes ! Read the book ..
I keep coming back to this statement.
Can you elaborate on how this causes problems condensing?
-
Check your gauges and thermometers. You can have all kinds of funny conclusions when your instruments are damaged.
The system either isn't condensing or is condensing at a pressure much lower than you think. Such as wrong refrigerant, R-22 instead of R-410a. Some jackleg filled an R-22 system with R-12. Nahhh.... not likely.
I'd check my gauges first and avoid looking like a fool. Then the thermometer.
Last edited by allan38; 03-30-2010 at 11:10 PM.
“I am for doing good to the poor, but...I think the best way of doing good to the poor, is not making them easy in poverty, but leading or driving them out of it. I observed...that the more public provisions were made for the poor, the less they provided for themselves, and of course became poorer. And, on the contrary, the less was done for them, the more they did for themselves, and became richer.”
― Benjamin Franklin
-
I had unit yesterday, that with my didgicool, measured -78 SC and 20* sh. High discharge pressure and high suction, going off on high head safety and compressor overheating. So I figured the condenser wasn't rejecting heat, although the fan was working. Cleaned condenser coil bc it looked pretty restricted, but shortly thereafter compressor seized up. 8year old rtu that had no PM.
-
 Originally Posted by INTECHBILL
This happens whenever the compressor absorbs heat instead of rejecting it ! Many causes ! Read the book ..
The compressor creates heat. It does not absorb heat! Not unless the entering gas temperature from the suction line is hotter than the compressor.
The refrigerant gas returning to the compressor either absorbs the heat produced by the compressor, or it will be to super-heated to absorb that heat, thus not helping cool the compressor. In short, the refrigerant removes the heat created in the compressor, (ie: Heat of compression), or the compressor will most likely overheat. (Assuming it does not have some other external means of cooling the compressor).
-
Undercharged? Dirty condenser fins?
-
But its still not the compressor that rejects heat. It only moves the vapor. Its u to the condenser to remove the heat of the vapor/hot gas discharge.
The return gas is what cools the compressor by absorbing heat from the compressor.
If the compressor is loaded with oil. You have another problem.
The condenser has to be more then restricted to cause a compressor to shut down on its IP. If the condenser fan is not working. Then its the condenser coil that is not removing heat.
Most medium temp compressors don't need liquid returning to them to remain cool.
But if they do. Then it is the refrigerant that is absorbing heat from the compressor. Not the compressor rejecting heat.
-
INTECBILL; IF the condenser is restricted the high pressure 'll increaes as well the compressor amps drawing , due to that , the widing temp 'll raise and the compressor overheats , but that does'nt mean than the compressor adsorbs heat. Anyways I think it could happen if the condenser coil is away too big, I had a similar situation with a chiller, the unit was a litte low in refregerant and the discharge line was conected to a heatexchanger to heat the water, so was over sodcooling the refregerant so at the end of the condenser the liquid line was aCtually cold and sweating.