Results 1 to 11 of 11

Thread: mp66

  1. #1
    Join Date
    Nov 2003
    Location
    South Carolina
    Posts
    1,167
    Post Likes
    Is everyone else using this for r12 drop in on walk in freezers to maintain 0 degree temp?

  2. #2
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    12,941
    Post Likes

    MP66 (R401B)........

    A short answer?.......No.

    It seems that most folks are going for R409A or more lately this HotShot stuff.

    If you are forced to retrofit an existing R12 low temp system MP66 is the best interim replacement performer out there, in my opinion.

    That being said, if you have an existing R12 walk-in freezer it must be nearly as old as dirt and long overdue for a complete system changeout. Sell the customer on a shiny new R404A system, collect your money and sleep well at night knowing you've done the right thing.

  3. #3
    Join Date
    Nov 2003
    Location
    South Carolina
    Posts
    1,167
    Post Likes
    Thread Starter
    Chinese restraunt...aint gonna happen...i guess i will be recharging with mp66...but they want it cheap...that aint gonna happen either...

  4. #4
    Join Date
    Nov 2003
    Location
    South Carolina
    Posts
    1,167
    Post Likes
    Thread Starter
    Actually this walk in freezer was installed in 1999. Tecumseh condensing unit but no where on this unit is their anything identifying what r12 alternative that they used. Its just listed as r12. Its in very new condition nothing very old. I have no idea why they installed an r12 system over 404.

  5. #5
    Join Date
    Jul 2001
    Location
    Gold Coast of Connecticut
    Posts
    4,849
    Post Likes
    r-12 or mp-66 is ALOT better on hot kitchen applications like yours. I love mp-66 it is a very good gas

  6. #6
    Join Date
    Jun 2001
    Location
    San Diego, CA
    Posts
    1,175
    Post Likes
    Converted a walkin last year. Required a TXV adjustment.
    I prefer it also to Hotshot however I find few using it.
    Run across more 414b retros.

  7. #7
    Join Date
    Feb 2003
    Posts
    1,171
    Post Likes
    Have not run across the need for MP66 in several years, glad for that. I'd recommend as previous and suggest complete replacement. They must've purchased some unit that sat for many years at the suppliers.
    Watts New, Ohm My, I been Electrically Commutated. Are U2.

  8. #8
    Join Date
    Feb 2004
    Posts
    126
    Post Likes
    HP-80 works really well too. Depends on the mood as to either 66 or 80.

  9. #9
    Join Date
    Nov 2003
    Location
    South Carolina
    Posts
    1,167
    Post Likes
    Thread Starter
    What type txv adjustment might i be looking at? Something tells me im gonna learn chinese by the time i leave that place tomorrow.

  10. #10
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    12,941
    Post Likes
    Originally posted by gdavis
    HP-80 works really well too. Depends on the mood as to either 66 or 80.
    HP80 is a low temp interim replacement refrigerant for R502. It's not even close to MP66 which is meant to replace R12 low temp. Don't get them confused or you'll be in for a surprise.

  11. #11
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    12,941
    Post Likes
    Originally posted by hackmaster
    What type txv adjustment might i be looking at? Something tells me I'm gonna learn Chinese by the time i leave that place tomorrow.
    You don't want to be messing with the TXV until it gets close to your desired temperature. Initial startup is a good time to be adjusting the CPR valve (if it has one).

    The time waiting for the box to pull down may well be spent reviewing your conversational Chinese handbook.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.