    txv frosted on waterfurnace

    ewo 42 waterfurnace superheat 55 degrees suction presssure 25 ,subcooling 10 degrees,head pressure265, td 1 deg, txv is frosting , ewt 33, unit shuts off on lp , txv is frosted ,thanx in advance

  2. #2
    Join Date
    Apr 2008
    Location
    Pa.
    Posts
    1,092
    r-22 or 410a? All I can say with the information provided is the txv is bad or theres a restriction at the txv.

  3. #3
    Join Date
    Jan 2009
    Location
    Baltimore
    Posts
    62
    If it's an "Envision" series,then 410a

  4. #4
    Join Date
    Jan 2007
    Location
    Beech Creek, PA
    Posts
    68

    Geothermal anyone

    See 265 psi on discharge pressure is telling me R-22 If that is the case i would agree with you but some more measurments need to be taken. Put a temp. probe on the out let of the evaporator i know this is a tight area to work and get measurements but it is possible. Pull the TXV sensing bulb off of the vapor line and hold it in your hand giving heat to the bulb should open the TXV and you should see your outlet of the coil temp. start to drop off. Then get a glass of ice water and put the bulb in the water you should see the temp. starting to rise since the bulb is wanting to close down. With these to simple test you can feel positive on a bad txv before i replace a txv those are always my procedures. If your unit is R410-a It sounds like an undercharge. Also with 33 deg. inlet water from the ground i would also be looking at you loop how efficient are we gathering heat/rejecting heat. 33deg. i have seen in the middle of the night on below freezing temps. unless this is a new unit it concerns me that you have such a low entering water temp.

  5. #5
    Join Date
    Dec 2005
    Location
    Indiana
    Posts
    277
    Is it an open loop? acid flush
    Work sucks, lets go skydive

  6. #6
    Join Date
    Jan 2010
    Location
    Fort Wayne, Indiana
    Posts
    97
    dfishinfool,

    (Posted in another HVAC-talk thread on 3/29/10)…

    “dfishinfool,

    We have read through your comments regarding the frosted TXV, and would like to be of assistance. Please let us know if you are an HVAC contractor or the homeowner. This information will be beneficial as we look into your inquiry further.

    WaterFurnace International, Inc”


    We will be more than happy to work with you to facilitate a resolution if our assistance is still needed.

    WaterFurnace International, Inc.

  7. #7
    Join Date
    Aug 2007
    Location
    Western Colorado
    Posts
    497
    Quote Originally Posted by dfishinfool View Post
    suction presssure 25 ,subcooling 10 degrees,head pressure265, txv is frosting,unit shuts off on lp ,
    Sounds like a restriction in the liquid line somewhere! Probably TXV, if the liquid line before it has no frost.
    RealEyes
    Realize
    RealLies!




  8. #8
    Join Date
    Dec 2011
    Location
    USA
    Posts
    66
    Water furnace had a rash of bad TXV's I would have a WF tech look at it the Envision series has a 10 year warranty

  9. #9
    Join Date
    Jan 2012
    Location
    Missouri
    Posts
    56
    Is just the txv frosting up? Whats the pressure drop on your loop?