    need help getting txv rating

    Hey everyone, hopefully someone will be able to help me out. I am trying to find specs for a sporlan valve. The valve is installed on a low temp evaporator, and the bulb is well mounted, this is a bohnmizer system. txv does not have any info on it other than y601 stamped on the body. the power element is a 33vc. If anyone can locate specs for this valve, it would be much appreciated.

  2. #2
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,514
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  3. #3
    Join Date
    Feb 2007
    Location
    Northern NJ
    Posts
    660
    thanks for the link cracker. I couldn't find what I needed there, but definetely a good resource.

  4. #4
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,147
    TJ

    hopefully andy will be along to help out. let me try to help a little, though. If this is a bohnmizer it is likely that you have a condensing unit without lowambient valves (ie flood master) I have seen these bohnmizer txvs for units that the factory designed for wide variances in head pressure. I think if all else fails, maybe what you could do is size a txv for the evap btuh at design temp and use a balanced port txv. any ides on condenser capacity?


    r404a

  5. #5
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,147
    http://hvac-talk.com/vbb/showthread....ight=bohnmizer



    may be of some help, maybe not. good luck.

    r404a

  6. #6
    Join Date
    Feb 2007
    Location
    Northern NJ
    Posts
    660
    r404a- thanks for the response. I do not have the complete condensing unit model number right now, partial is EB31L. 30 horsepower, I believe. This was at one time a freezer, and is now a cooler, using a cpr valve. I forgot to mention earlier r-22 and power element 33VC. As you stated, there is no condenser flooding. 4 condenser fan motors- 2 on the header end run all the time, the two on the return bend side cycle on individual ambient tstats. Evap model FL10503H.

    some operating conditions- 62 outdoor ambient condenser running 2 fans 175liquid pressure suction 30 at evap 19 at compressor side of cpr. 8 degree subcooled liquid at evap. 17 degree superheat at evap, valve wide open. 31 degrees superheat at compressor. compressor amps 34/34/38 rated load 47.

  7. #7
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,987
    It's a Bohnmizer TEV... one of the original balanced port TEVs Sporlan manufactured. This design was made exclusive for Bohn.

    Sporlan allowed Bohn to size the valves as they see fit. As r404a notes, these valves were oversized to handle low ambient operation.
    If the only tool you have is a hammer, you tend to see every problem as a nail. Abraham Maslow

  8. #8
    Join Date
    Jan 2010
    Posts
    6,838

    Andy

    Andy
    Not to hijack thread but maybe you could help out Wannafreeze with his problem ?