    Spyder Nvo_Io proxy points Problems

    Some of my nvo_Io UI's are not working properly. The ones i am noticing are for temperatures. Some of them are reading much lower than they should. This is happening on several controllers. I have multiple temps on each, some come out ok, and the others are around 50 degrees less. All the facets are the same as compared to the ones that are working. Is this a known problem, and should i just create individual nvo's for each temp rather then using the nvo_io points?

  2. #2
    Join Date
    Aug 2007
    Location
    Western Colorado
    Posts
    497
    Did you verify that a 20k ohm sensor was attached to the UI?
    And that you changed the default data type from Celsius to Fahrenheit?
    RealEyes
    Realize
    RealLies!




  3. #3
    Join Date
    Jan 2005
    Location
    USA
    Posts
    1,450
    Dont forget to change conversion to linear after bringing the points out. I have had to re-proxy some points in the past for unknown reasons. Spyders are still glitchy in that aspect.