    I wonder why your boiler is air bound?

    Complaint was short cycling plus they kept hearing water in the lines. I sold the job and will be installing it within the next few days. I will post the after results then.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	IMG_2204.jpg 
Views:	722 
Size:	49.3 KB 
ID:	86602   Click image for larger version. 

Name:	IMG_2205.jpg 
Views:	587 
Size:	53.4 KB 
ID:	86612   Click image for larger version. 

Name:	IMG_2206.jpg 
Views:	583 
Size:	52.3 KB 
ID:	86622   Click image for larger version. 

Name:	IMG_2207.jpg 
Views:	561 
Size:	50.5 KB 
ID:	86632  
    Any fool can know. The point is to understand. Albert Einstein

  2. #2
    Join Date
    Oct 2001
    Location
    Comstock Park Michigan
    Posts
    100
    I bet that circ pump works really well with that st. 90 on it. :?
    We do it nice cause we do it twice!

  3. #3
    Join Date
    Dec 2007
    Posts
    3,853
    I am no boiler person, see one or two a year, so can you explain what all is wrong so I can educate myself?

    thanks

  4. #4
    Join Date
    Feb 2010
    Location
    Northeast, PA
    Posts
    235

    Amazing

    I blows me away that the boiler ran for years, and the piping is a mess. The manufacturer sends that "little booky thing" IOM to try and avoid a moron from piping it that way. Scary isn't it! Good pics.

  5. #5
    Join Date
    Jan 2008
    Location
    Outside The Motor City
    Posts
    657
    Yaaaa! I remember when I had my first beer.
    NO Brains NO Headaches

  6. #6
    Join Date
    Jun 2007
    Location
    Jersey
    Posts
    157
    Quote Originally Posted by pacnw View Post
    I am no boiler person, see one or two a year, so can you explain what all is wrong so I can educate myself?

    thanks
    The expansion tank is just there for looks, not being used really. The check valve (brown fixture before expansion tank) will not allow water to get into expansion tank. There is no air separation in this system such as an air scoop. The air vent is not helping the system where it's placed. The circulator although in an ok spot should not have a street 90 right before going into the pump. The boiler/ setup is over 25years old this is how it should look like now or at least in my opinion... http://www.bellgossett.com/homeowner...flo-Module.asp
    Any fool can know. The point is to understand. Albert Einstein

  7. #7
    Join Date
    Jun 2004
    Location
    Western MA.
    Posts
    477
    I`ve actually seen expansion tanks piped this way and they worked fine,as long as the pump is running.

    Not saying this is how I would do it.
    I love overtime I just hate working for it.

  8. #8
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,745
    While the whole job is laughable at best, there's really nothing wrong with the expansion tank, per se. The flow valve is open to the check through either the bottom or back port. The only port that's affected by the check/flow valve is the port that's going out to the system. I admit to, on occassion, taking an addional loop off the back of a check valve like that when the customer needed a new loop and the cost of repiping would be a job killer. Of course, that was always with a circulator on the return, not on the supply pumping away.
    If YOU want change, YOU have to first change.

    If you are waiting for the 'other guy' to change first, just remember, you're the 'other guy's' other guy. To continue to expect real change when you keep acting the same way as always, is folly. Won't happen. Real change will only happen when a majority of the people change the way they vote!

  9. #9
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,092
    What scares me most about the setup, is loop in below boiler with no low water cut off and/or flow switch.

  10. #10
    Join Date
    Oct 2008
    Location
    Brewster, MA
    Posts
    121
    Although I personally would never install anything as crude as this, from a technical standpoint, it is correct or was at the time of install.

    When this was installed, circulators came installed on package boilers on the return. When installed on the return, you do not get cavitation and air in the supply side like you do now with "pumping away" installs. There was a reason circulators were put on the return back when. With wet seals, they didn't fail as quickly as ones on the hot supply.

    As far as the piping below the boiler, all piping, supply and return go above the boiler. It could have been installed higher but it does go over the top. A low water cut off would be nice.

    There should have been a vent at that evil street ell. Like a float vent. The water noise was more likely from air/water in that section and the circulator pulling against it.

    I would have put the boiler feed on the return at the boiler so water fed directly in to the boiler and installed a valve between the boiler and purge valve on the return for ease of purging. If something happened to the below piping, the boiler would always be filling first to get to the leak.

    One can nit-pick something to death but it is essentially correct.

    One can crow the sunrise up about circulators on the supply but they don't always work as advertised.

    Works for me.

  11. #11
    Join Date
    Jun 2007
    Location
    Jersey
    Posts
    157

    The new boiler

    I changed out the boiler. Very simple job. Feel free to comment. I am here to learn. I did put the drip leg for the backflow preventor and changed the gas flex the next day.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	IMG_2208.jpg 
Views:	121 
Size:	55.7 KB 
ID:	87942   Click image for larger version. 

Name:	IMG_2209.jpg 
Views:	93 
Size:	49.0 KB 
ID:	87952   Click image for larger version. 

Name:	IMG_2210.jpg 
Views:	101 
Size:	46.9 KB 
ID:	87962   Click image for larger version. 

Name:	IMG_2211.jpg 
Views:	98 
Size:	46.5 KB 
ID:	87972   Click image for larger version. 

Name:	IMG_2212.jpg 
Views:	110 
Size:	44.8 KB 
ID:	87982  
    Any fool can know. The point is to understand. Albert Einstein

  12. #12
    Join Date
    Feb 2010
    Location
    Northeast, PA
    Posts
    235

    Smile

    Looks good and has straight pipes, You cheated, you own a bullet level and a ruler dont you.

  13. #13
    Join Date
    Feb 2010
    Location
    Northeast, PA
    Posts
    235
    More compliments for not destroying the top of the boiler with solder blobs and tool scratches. BRAVO!!!!!

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •