  1. #1
    Join Date
    Jul 2002
    Location
    NorthEast
    Posts
    811

    saving/downloading controlers to Johnson NCM workstations

    I added a DX controler to an NCM.I saved the file on the PC workstation,that holds all of the archive files.
    What is the proper procedure for the following?
    I want to save the file on a memory stick.
    load that file on the other two Workstation PC's.
    As of now the other two PC's see the controler in a seperate system file,at
    the bottom of the directory tree,and not in the actual 9th Floor folder.
    If I recall I have to use DOS to decompile the DDL. File to save it.and then recompile it to download it to the PC.
    Thank you

  2. #2
    Join Date
    Mar 2008
    Location
    NW Ohio
    Posts
    949
    You should put some effort forth.

    It is clearly detailed in the OWS User's Manual

  3. #3
    To put a file on a memory stick, I use the drag drop method. You could use copy paste method to. The same will work go from memory stick.

  4. #4
    If you perform modificatetions to the map all of the screens would look the same.

  5. #5
    Join Date
    Jul 2002
    Location
    NorthEast
    Posts
    811
    Actually it is in the DDL programming Manual
    The dos Coommand to compile is
    DDL sourcefilepath.ddl

    To un compile
    UNDDL sourcefilepath.und

  6. #6
    Join Date
    Mar 2008
    Location
    NW Ohio
    Posts
    949
    Quote Originally Posted by cleancondenser View Post
    Actually it is in the DDL programming Manual
    The dos Coommand to compile is
    DDL sourcefilepath.ddl

    To un compile
    UNDDL sourcefilepath.und
    Really? You must be a metasys ddl'ing genius now.

    You're almost completely clueless on this matter.
    Yes, your original nonsensical ramble could be done with ddl, but it would be much safer for someone that is trying to become a novice, to use the OWS method. But, by all means, proceed at will.

    Here are some guesses on your future thread titles.
    -What's the syntax for the unddl command?
    -Hey, where did my unddl file go?
    -I found my unddl file, now what?
    -My ddl file won't compile, what does this error mean.
    -My ddl compiled, but everything still looks the same, what up with that?
    -What happened? All of my passwords and schedules are missing.

  7. #7
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    1,472
    Quote Originally Posted by NINAX View Post
    Really? You must be a metasys ddl'ing genius now...You're almost completely clueless on this matter....
    Ouch, that's gonna leave a mark !

    cleancondenser, the method in the OWS Users manual is much safer. Doing it in "DDL" can cause some huge problems if you even make a very small mistake.

    Simply adding a new system to each additional OWS would have only taken a couple of minutes and had very small risk involved in regrads to the N1 network. Be very careful using DDL on a system.
    Last edited by Cagey57; 03-26-2010 at 03:55 PM.
    If sense were so common everyone would have it !

    All opinions expressed are my own. Any advice provided is based on personal experience, generally accepted fact or publicly available information. As such, it is worth exactly what you paid for it, not a penny more not a penny less !!

  8. #8
    Join Date
    Mar 2007
    Posts
    276
    Quote Originally Posted by cleancondenser View Post
    To un compile
    UNDDL sourcefilepath.und
    Not thru !! When you unddl then there is no sourcefile.... It gets created

    If all you want to do is to move the DX system to a your 9th Floor Group on the other 2 computers. Then simply go to each computer highlite the DX system and under Setup, select "Modify Group Assignment"

    As stated before: the OWS method is the safest way to accomplish these task for a novice Metasys operator.

    You can go the ddl route, but be careful.... you won't be the first one to wipe out all passwords, calender entries, report/access groups, ip numbers and workstation settings with one mouseclick

  9. #9
    I somewhat know what I am doing with PMI, and going the ddl path is still like handling wet dynamite to me. If you screw up...oh boy ..you could get screwed faster than a altar boy at the vatican.

  10. #10
    Were you able to copy your files on the other drive with out any issues OK?

  11. #11
    Join Date
    Sep 2006
    Location
    Alaska
    Posts
    475

    DDL

    If you decide to pursue the DDL route, first read the first the Data Definition Language. Although I agree with freddy-b that it's really dangerous in experienced hands. Here's the steps

    1) Upload the Global database at the archive OWS.

    2) UNDDL the Global database at the archive OWS. If you have errors than you will have to correct them first.

    3) Rename the Global file extension from GLOBAL.UND to GLOBAL.DDL

    4) Copy it to a diskette.

    5) Recompile the Global.DDL file

    6) Download the Global database at the archive OWS.

    7) Shut down Metasys and disconnect each of the non-archive OWSs from the LAN.

    8) Compile the archives Global .DDL file on each non-archive OWS.

    9) Start Metasys and download the Global database on each non-archive OWS.

    10) Shut down Metasys, and delete the online Globrev.dbf (e.g., C:\Project\Contract\Netname\Globrev.dbf) file on each non-archive OWS.

    11) Restart Metasys on each non-archive OWS.

    12) Reconnect each non-archive OWS to the LAN.
    Law Of The Thermostat: He who has the thermostat wins!!!!!

  12. #12
    Join Date
    Mar 2008
    Location
    NW Ohio
    Posts
    949
    Quote Originally Posted by simux View Post
    If you decide to pursue the DDL route, first read the first the Data Definition Language. Although I agree with freddy-b that it's really dangerous in experienced hands. Here's the steps

    1) Upload the Global database at the archive OWS.

    2) UNDDL the Global database at the archive OWS. If you have errors than you will have to correct them first.

    3) Rename the Global file extension from GLOBAL.UND to GLOBAL.DDL

    4) Copy it to a diskette.

    5) Recompile the Global.DDL file

    6) Download the Global database at the archive OWS.

    7) Shut down Metasys and disconnect each of the non-archive OWSs from the LAN.

    8) Compile the archives Global .DDL file on each non-archive OWS.

    9) Start Metasys and download the Global database on each non-archive OWS.

    10) Shut down Metasys, and delete the online Globrev.dbf (e.g., C:\Project\Contract\Netname\Globrev.dbf) file on each non-archive OWS.

    11) Restart Metasys on each non-archive OWS.

    12) Reconnect each non-archive OWS to the LAN.
    Assuming it was worth it (more than one System that needed a PC Group change), if you really understand PMI and it's data structure, one could accomplish the same in 5 steps. And you'd never ddl anything, disconnect PCs, or reboot software.

  13. #13
    Join Date
    Jul 2002
    Location
    NorthEast
    Posts
    811
    Thank you Simux
    A former Johnson Tech demonstrated it your way.
    He did tell me of his stories of where he lost passwords and other data.
    This is not something I will be doing every day,but it is good to know.
    Appreciate all the help.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event