    Brazing in a fully charged system

    If you use a couple of ball valves in line with a liquid line dryer, one before and one after the dryer so you can isolate and change the dryer without having to recover the charge, should you use a flare connection to attach the dryer or braze it in? If you braze the dryer in how far from the valve would you place the dryer in order not to adversely effect the refrigerant in the liquid line while brazing?

  2. #2
    Join Date
    Mar 2010
    Location
    Houston
    Posts
    213
    Post Likes
    The ball valve thing seems to me a bad practice unless you have a schrader on the dryer to evac.

    I never like fittings where I can solder. Adds cost in brass fittings.

  3. #3
    Join Date
    May 2001
    Location
    Bennington, Vermont U.S.A.
    Posts
    13,856
    Post Likes
    Quote Originally Posted by rubafish View Post
    If you use a couple of ball valves in line with a liquid line dryer, one before and one after the dryer so you can isolate and change the dryer without having to recover the charge, should you use a flare connection to attach the dryer or braze it in? If you braze the dryer in how far from the valve would you place the dryer in order not to adversely effect the refrigerant in the liquid line while brazing?
    If you shut off the valves on either side of the drier you are still going to have refrigerant in the drier and the connecting pipe. You have to relieve that pressure/refrigerant before you put the heat to the drier.

    That little bit of refrigerant will build a lot of pressure when heated. You should always vent any vessel when brazing. If you shut the valves and drilled a hole in the drier that would be safer. But I reccomend using a flare drier to do what you want to do.

    Most condensing units are properly valved so that you can pump-down the system and change the drier without losing the charge. So I don't know why you are trying to do what you are describing.

  4. #4
    Join Date
    Feb 2009
    Location
    Brightion Michigan
    Posts
    31
    Post Likes
    sounds like a bad idea.you are just asking for problems what if someone or something closed the valves. and you cant be certain that all moisture or air are not going to be removed from the system.and if using fittings that thay might leak over time.best bet would be to remove the refrigerant. or pump down. braze the new dryer in. nitrogen. and vac the unit.then weight in new refrigerant.

  5. #5
    Join Date
    Mar 2008
    Location
    wi
    Posts
    282
    Post Likes
    Iv'e seen that done alot on large cond units but they all had schrader ports, what I did was recover the refrigerant into the suction line, take apart the filter housing replace the filter core(s). Evac and move on

  6. #6
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by wildtech View Post
    Iv'e seen that done alot on large cond units but they all had schrader ports, what I did was recover the refrigerant into the suction line, take apart the filter housing replace the filter core(s). Evac and move on
    Ditto that.

    On the larger equipment that I work on, removing the entire charge is largely impossible and definitely impractical.

    On smaller, residential sized condensing units, it is possible, but what would it be worth? If you are that worried, a single liquid valve, a flare drier and a few tools would accomplish the same thing.

    Heck, if you wanted to get REAL fancy, you could pipe a 3 valve bypass arrangment, allowing you to change the drier 'on the fly'. I have that setup on some of the newer equipment. No need to do a big pump down, just close 2, open 1 and pump it out. Driers in and out in maybe 15 minutes.



  7. #7
    Join Date
    Jan 2010
    Location
    Jacksonville Beach, Fl
    Posts
    120
    Post Likes
    Thread Starter
    Let me be alittle clearer on what I'm concerned about. After replacing a locked compressor I want to put in a liquid line dryer to clean up the system and protect the compressor. I want to be able to change this filter at a later date without having to recover the charge so I plan on using ball valves to isolate the dryer from the system. I am concerned that if the dryer is too close to the full charged liquid line on the other side of the ball valve, not the side that the dryer is on, will I expose this line to too much heat while brazing in a replacement dryer?

  8. #8
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    how do you plan on flowing nitrogen while brazing in the new drier?

    sounds like a bad idea, just pump the unit down at the service valves.

  9. #9
    Join Date
    Jan 2010
    Location
    Jacksonville Beach, Fl
    Posts
    120
    Post Likes
    Thread Starter
    I would put in some schraders but recovering the charge then replacing the dryer sounds like the best way to go.

  10. #10
    Join Date
    Apr 2008
    Location
    Pluto
    Posts
    984
    Post Likes
    What he asked above, how do you plan on flowing nitrogen while brazing in that new drier?
    Not as lean, not as mean, but I'm still a hardcore, ass-kicking, hard charging Marine! Oohrah!

  11. #11
    Join Date
    Jan 2010
    Location
    Jacksonville Beach, Fl
    Posts
    120
    Post Likes
    Thread Starter
    Through the schrader. This set up would allow me to change the dryer on the fly. I would place the dyer in the liquid line so that it see liquid in both heating & cooling modes. On opposite sides of the dryer I would put a ball valves with schraders on the dryer side which would allow me to recover the refrigerant from the filter before changing. It would also allow me to flow nitrogen while brazing. But I am still concerned about the heat transfer along the liquid line passed the ball valve to the charged side of the system while brazing so I'm not going to do this.

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Use refrigeration valves that require a wrench to shut and open them, along with either filters that have schraders, or install an access fitting so you can check to make sure you have the refrigerant pumped out.

  13. #13
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    If you are that dedicated to changing the drier, install a replacable core type.

    No nitrogen needed.



  14. #14
    Join Date
    May 2001
    Location
    Bennington, Vermont U.S.A.
    Posts
    13,856
    Post Likes
    I don't get it. What capacity is this system? Is this a RTU and it has no service valves?

    Okay I'm going out on the limb here. If you pump down a system. Have the new drier already to be brazed into the line. Then I would, check and make sure there is no pressure left in the liquid line. Vent the liquid line through the service port of the service valve. Quickly un-sweat the old drier and braze in the new one. Without a nitrogen purge.

    Then pull a vacuum. Charge the liquid line. Open the service valve and you are done.

    I contend that the liquid line will only have vapor in it during this process. No air will enter the line during this process. Therefore there is no need to purge nitrogen during a simple drier change.

    (there this ought to start a discussion.)

  15. #15
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    If you are that dedicated to changing the drier, install a replacable core type.

    No nitrogen needed.
    Ditto that, or go with two refrigeration valves (that must be operated with a wrench) and flare the pipes feeding the drier. Use a liquid line drier with a schrader, or just sweat one onto one of the lines between the valve and the drier if you don't want to be stuck with always buying a drier with a schrader on it.

    Caveat with replaceable core driers...install them correctly so they don't become oil traps.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  16. #16
    Join Date
    May 2004
    Location
    Toronto
    Posts
    276
    Post Likes
    putting valves on both side of the drier would require a safety valve to be installed between the valves so the drier doesn't become a bomb

  17. #17
    Join Date
    Jan 2004
    Location
    Earth
    Posts
    4,880
    Post Likes
    Quote Originally Posted by benncool View Post
    I don't get it. What capacity is this system? Is this a RTU and it has no service valves?

    Okay I'm going out on the limb here. If you pump down a system. Have the new drier already to be brazed into the line. Then I would, check and make sure there is no pressure left in the liquid line. Vent the liquid line through the service port of the service valve. Quickly un-sweat the old drier and braze in the new one. Without a nitrogen purge.

    Then pull a vacuum. Charge the liquid line. Open the service valve and you are done.

    I contend that the liquid line will only have vapor in it during this process. No air will enter the line during this process. Therefore there is no need to purge nitrogen during a simple drier change.

    (there this ought to start a discussion.)
    I agree, no need to over complicate things.
    A Diamond is just a piece of coal, that made good under pressure!

  18. #18
    Join Date
    Oct 2005
    Location
    Pacific Northwest
    Posts
    2,551
    Post Likes
    Flare it in. Ball valves/schrader port optional. Allows for any type of swap later.

  19. #19
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes
    I have done this on voyager units. Place a ball valve on both sides of the drier, and braze in flare nut stubs. If it is a LL drier, use a "t" and braze in a pressure port. On the suction side, use a drier with a schrader port in it.

    It is much cheaper for the customer to do this rather than pay for another recovery, and vacuum.

  20. #20
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes
    Quote Originally Posted by benncool View Post
    I don't get it. What capacity is this system? Is this a RTU and it has no service valves?

    Okay I'm going out on the limb here. If you pump down a system. Have the new drier already to be brazed into the line. Then I would, check and make sure there is no pressure left in the liquid line. Vent the liquid line through the service port of the service valve. Quickly un-sweat the old drier and braze in the new one. Without a nitrogen purge.

    Then pull a vacuum. Charge the liquid line. Open the service valve and you are done.

    I contend that the liquid line will only have vapor in it during this process. No air will enter the line during this process. Therefore there is no need to purge nitrogen during a simple drier change.

    (there this ought to start a discussion.)
    Most commercial package units dont have service valves.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •