    Carrier 30XA Air Cooled Screw Chiller WTF!

    I'm having an awful time trying to maintain a pair of these so-called pieces of refrigerating machinery that are installed in Upstate, NY.

    Mysterious refrigerant leaks

    Suction Service valves that ROAR refrigerant out of them when it gets cold, then hold tight when you look at them differently? haha.

    The panel on the unit says each circuit holds 300lbs R-134a each. Then if you check the Carrier manual it says they hold 240lbs each when used with the flat plate condensers (which I have)

    So after I removed what little charge was left in each circuit, made leak repairs, and recharged them according to the Carrier manual, Now I'm getting HIGH PRESSURE trips.

    How about ICE BUILDING ON THE Wye Delta starter contactor interlock and preventing that circuit from starting!

    Anyone have this kind of BS happen on these things?

    Is the Touch Pilot the worst control interface? Or is it just me?

    Is it even REMOTELY POSSIBLE to work on the controls without getting electrocuted based on the disgusting manner in which they were wired?! The electrical panel is right on the ground with all the wiring STUFFED up behind all the components??

    How about the control power transformer that's wired on the LOAD SIDE of one of the compressor breakers, that way if you want to work on that compressor, it kills control power to the ENTIRE MACHINE!

    Discharge isolation ball valves. REALLY. They all open on machine startup even if only one compressor is going to run? What's the point of that then?


    Comments from Carrier guys? People with experience?

    Thanks fellas for the discussion.
    Perspicacity

  2. #2
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,550
    You know when I go to work on a piece of equipment I make it a good practice to write down the model and serial number on every piece of equipment that I work on.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  3. #3
    Join Date
    Mar 2003
    Posts
    7,253
    you got a bad attitude. you just dont understand. we dont do business like that, its too expensive. we have never needed to do that. we have never heard of anyone having that problem. you need to change that inlet screen, really the check valve holds everytime. i have heardevery reason whythese machines are not a problem, except the real ones. Bottom line, manufacturers today make things to compete on price, not to be easy for us to work on each day. the reality is that clients get pissie due to spending waay too much money on repairs due to some of your issues, and others, BUT, first cost was less, so get over it and take their money. WAIT, i forgot my favorite one....we pressure tested that befor it left the factory! anyone ever been to a factory to see a pressure test. they take the coil or whatever and filll it with compressed air at 300 psig, then lower it into a tank of water and look for bubbles for crying out loud. like they really care. then they use about a four hundred cfm pump to evacuate, and finally dump some gas in dere, an amount determined only by reading a scale.

  4. #4
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,550
    Quote Originally Posted by flange View Post
    you got a bad attitude. .
    Who are you referring to there Flange?
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  5. #5
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,460
    Did you ever notice when somebody can't fix something that it automaticly becomes a piece of crap no matter who make it.
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !

  6. #6
    Join Date
    Jul 2009
    Location
    In a mechanical room....
    Posts
    1,879

    Hmm

    Obviously he had a bad day and is just venting. Everyone has those days...

  7. #7
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,460
    True we have all been there not every day is a bed of roses its called murphys law anything that can go wrong usually will and usually does.
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !

  8. #8
    Join Date
    Apr 2006
    Location
    mechanical room
    Posts
    1,224
    well, he is right, not my favorite machine either

  9. #9
    Join Date
    Mar 2003
    Posts
    7,253
    i wasnt referring to anyone. the first few comments in my post were things ive heard people say over the years to thers who were complaining about these machines. ever walk up to one that was VE'd, and didnt have isolation valves to dump the charge in the condenser?, or hadnt had the screen replaced EVER, let alone after the recommended five hundy hours of runtime, and see oil failure afte oil failure? the reality is that the vast majority of manufacturers are now trying to compete with each other on price, and we, the collective field guys suffer. they just dont make em like they used to. the client *****es about time, we ***** about serviceability, and so on.

  10. #10
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    if there maintained and kept up they last a lot longer

    as well as work much better



    .

  11. #11
    Join Date
    Jun 2007
    Location
    NY
    Posts
    37
    Quote Originally Posted by york56 View Post
    True we have all been there not every day is a bed of roses its called murphys law anything that can go wrong usually will and usually does.
    Well... it seems you had a premonition Mr. York...

    I was venting this morning before I took a service call to this FULL MAINTENANCE customer. This is probably the most ridiculous thing I've ever seen in my short amount of experience, and pretty much takes the cake with this piece of equipment.









    THAAAAAT'S RIGHT... TWO FAN MOTORS WITH THE FEET RIPPED RIGHT OFF!!

    The only thing that kept it from falling and blasting through the condenser was the goofy "Ultra quiet" fan blades and housings that Carrier uses. It also destroyed the contactor to the fan before the breaker tripped because neither motor had shorted to ground.

    I have no less than 3-4 weeks of time into these machines in the last year and a half.
    Perspicacity

  12. #12
    Join Date
    Jun 2007
    Location
    NY
    Posts
    37
    Quote Originally Posted by thegoodlistener View Post
    You know when I go to work on a piece of equipment I make it a good practice to write down the model and serial number on every piece of equipment that I work on.
    m/n 30XAA3506C-05JFC
    s/n 3107Q91627

    m/n 30XAA3506C-05JFC
    s/n 3007Q91625

    Perspicacity

  13. #13
    Join Date
    Aug 2009
    Location
    Fort Lauderdale Fl
    Posts
    282
    Hey 2 outa 4 isnt that bad if you think about it