    Liebert Minimate Plus

    I had walked past the condensing unit for this set up for 10 years and never gave it a second glance until 2 weeks ago. We traced out the refer lines an found the evaporator unit in the drop ceiling. No one had any idea it was there. Once I began troubleshooting the unit, I have 208V coming into the unit, 24V out of the transformer and into the circuit board, but no voltage anywhere else on the board. I pulled the board and see no signs of damage. I am thinking it is a bad circuit board? Any one have any insight on what I might be overlooking? This is the first time I have worked on a unit like this.

  2. #2
    Join Date
    Feb 2010
    Location
    Russia
    Posts
    44
    Post Likes
    And no fuse in the circuit board?

  3. #3
    Join Date
    Feb 2015
    Location
    Kodiak Alaska
    Posts
    21
    Post Likes
    Not that I can see anywhere.

  4. #4
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,331
    Post Likes
    Can you post a picture of the control board?


    Sent from my iPhone using Tapatalk

  5. #5
    Join Date
    Feb 2015
    Location
    Kodiak Alaska
    Posts
    21
    Post Likes
    Turns out to be a loose connection on the circuit board and 4 wires disconnected from the room temperature sensor. Made all the connections correctly and this unit ran for the first time in at least 10 years.