Thread: Highest S.H.

  1. #1
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084
    Just curious..(I need ammo), what's the highest superheat on LT 22 rack seen(at comp) without tripping demand cooling.



  2. #2
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215
    I've seen them at 90 degrees or more not tripping the DC switch, OFTEN.

    As far as NEVER tripping them, as far as I know, 50-60 degrees probably would hold for a long time.

    I've also seen a lot of failed DC controls that didn't fail tripped, so it's hard to say at what point you can start frying eggs on the heads....

    Not a good idea to run them over about 30 degrees, though.

  3. #3
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084
    I have a H.P. rack at 90* now.When it was first started up ,we had the end bells at 35*.Rack ran great. Then the store's refrigeration consultant came through and was whining about the ice on the suction lines.He wanted it all gone. We tried to tell him that ice is a good thing.....well he got his way.Thursday the D.C. started tripping. I found a 4D with a bad plate gasket.

    I told the manager get ready for summer.

  4. #4
    Join Date
    Apr 2002
    Location
    most of the time in the Philippines
    Posts
    1,211
    Consultant- someone who borrows your watch to tell you the time.

  5. #5
    Join Date
    Jan 2004
    Location
    Earth
    Posts
    4,879
    Does that DC cycle or does feed all the time. With that head gasket blown I would think it was always on.

    If your DC does not cycle you are gonna have problems with tripping. Your also gonna have problems with that compressor.

    Not to mention the load your sacrificing with all that additional work the DC is causing. Demand cooling is a good thing, but it is not without it's cost. Your comp has to pump that extra gas.
    A Diamond is just a piece of coal, that made good under pressure!

  6. #6
    Join Date
    Jul 2001
    Location
    Gold Coast of Connecticut
    Posts
    4,571
    DC cycles on the temp of the discharge via that little probe in the head. If turn on when hot then cycles off. I have NEVER seen one continously. Maybe you needs a new DC module or sensor.

  7. #7
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215
    Nope. They need to put the SH back where it was, and get rid of the frost-fearing consultant.

    90 degrees is a pump killer.

  8. #8
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215
    I belive that the switch trips on continuous feed. I'll have to look that up, though.

    I can't recall ever seeing one feed all the time/

  9. #9
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084
    Originally posted by condenseddave
    I belive that the switch trips on continuous feed. I'll have to look that up, though.

    I can't recall ever seeing one feed all the time/
    It does..that's why the DC reset.The head gasket was blown on the sensor head(was reading 255*),the other head was 50-60* cooler. The DC was constantly running then would trip.

    I was taking infa-red readings on the front of the heads,where the discharge gas exits comp.

    Love that I.R.

    By the way it was fixed that day...I just wanted to see how high you have seen them(superheat)

  10. #10

    Oh, that poor motor...

    Don't forget that high SH doesn't just cause high discharge temp, but also might cause the motor to overheat and trip. The Copeland envelope is based on 65F RG. At -25, 90F SH is right on the edge. There is no good reason to run more than 50-60F SH on a low temp rack, and at those temps you will likely see frost...but no liquid. Frost is not the enemy.

  11. #11
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215
    Yup, don't fear the frost, the frost is your friend.

  12. #12
    Join Date
    Jan 2004
    Location
    Earth
    Posts
    4,879
    Emerson, do you know what the parameters for a compressor module to open are?

    I have seen compressors with a a 500 ohm difference between thermistors run.

    How much differance can there be, before the module opens.

    I believe the thermistors are rated 500 ohms dead cold, and 20,000 ohms cooking bacon. what is the trip point?

    Thanks in advance
    A Diamond is just a piece of coal, that made good under pressure!

  13. #13
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215

    From Copeland pdf on Motor protectors



    I highlighted the important part, hope it's legible, that's about as small as I can make the page and still not blow half Don's bandwidth...

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event