Thread: R-402b for ice machine??

  1. #1
    Join Date
    Feb 2003
    Location
    Laurens, SC
    Posts
    327
    Post Likes
    Working on a ice machine with R-12. CC Dickson co. told me that R-402b was recomended by the manufacture for replacement. Anyone used this stuff?? I noticed that it has propane in it. Thought that wasn't good. And as for charging a unit with a blend do you just charge it as a liguid on the low pressure side? Thanks for all the help. Kevin




    Sorry I meant R-402a instead of b. There are way too many diff. kinds out there.

    [Edited by 55fordtruck on 04-29-2004 at 09:07 PM]

  2. #2
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes

    Hmm 402B

    WAS the recommended replacement for 502 in Manitowoc ice machines, when they came out with their "B" series, which was the only mass-produced piece of equipment that used this crap-in-a-can.

    It is not even close to R12 on the PT chart, and is expensive as all gitout.

    I would go with 134a, or, if you're so inclined, 401B, aka "MP66", which is an HCFC replacement for low temp R12.

    My first choice is definitely 134a.

    Well, actually, my first choice with an R12 ice machine, would be recover, tag, and dispose. Then replace with something new, anything new. Well, anything new EXCEPT a Cornelius.

  3. #3
    Join Date
    Jan 2002
    Posts
    1,895
    Post Likes
    manitowic used it for a couple of years(hp81), yes it needs to be charged as a liquid however is the machine worth it ? daves right its way closer to 502 than 12

  4. #4
    Join Date
    Apr 2004
    Posts
    29
    Post Likes

    402B

    402B is still used by manitowac ive had pretty good luck with it. You can buy it in a small can of like 14lbs i think it is. Has to be charged as a liquid but you should be able to weigh it in through the high side from a vacuum. Just weigh in 80% of what the unit took for R-12 then run the unit. It should only take about 12-17 mins to make a batch of ice so start checking superheat @ the compressor around 8-10mins into the cycle. Adjust the charge as needed, should be around 10-12F superheat @ the compressor just before going into harvest. Assuming everythings clean and the space its in is with normal operating temps.

    Good Luck
    Bill

  5. #5
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes
    Which currently produced machine is manitowoc useing HP81 in?

    You can buy it wholesale in 13 lb. cans. It's going for about 15 bucks a pund, though.

    Why would ANYONE want to retrofit TO this expensive crap-in-a-can?

  6. #6
    Join Date
    Feb 2003
    Location
    Laurens, SC
    Posts
    327
    Post Likes
    Thread Starter
    Here's what I found out with more research. Manitowoc recomends for the R-12 machine (ED0402A) that I'm working on that I need to replace the TXV for MP39(401A), dump the oil out of the compressor and replace with Alkylbenzene oil. Then add the proper amount ou MP39. The machine that I'm working on holds 22oz. of R-12. Manitowoc's chart says to put 15oz of MP39 in. The head pressure will be 5-35#'s higher and low side 3-5#'s higher. Hope this helps anyone in the future. Also as for the R402b that is to replace R-502 machine's. Thanks for the help. KEVIN

  7. #7
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes
    408 is a better bet for any 502 icemaker.

    Manitowoc is still indignant that the industry didn't fall in line behind them and make HP81 the chosen refrigerant for 502 ice machine retrofits. Too bad.

    408 and 502 are near identical throughout the entire PT chart.

    HP81 isn't anywhere near the refrigerant that 408 and 404 are are, plus, you can expect a serious increase in discharge temperature with 81, which you won't see with 408.

    MP 39 might work fine in an R12 icemaker, but I'd be more inclined to change to MP66, IF I found an R12 Manitowoc that still had an evaporator that wasn't shot, and that is a rare find.

  8. #8
    Join Date
    Apr 2004
    Posts
    29
    Post Likes

    My appologies condenseddave

    No machine is currently being produced with 402b, but Manitowoc did produce machines with 402b i think this was in the late 90s have to check to be sure but I have 2 or 3 still running with 402b, trouble free.

    Ive also used as a 502 replacement but this was in a case where we were running a box temp at like -30 in a enviromental chamber.

    Wasnt a fun changeover though being 402b requires oil change

    Bill

  9. #9
    Join Date
    May 2004
    Posts
    2
    Post Likes
    I have used 414-B in R-12 ice machines with good results. It also goes under the name hot shot. Did not have to change oil or anything.

  10. #10
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes

    HP81..........

    Manitowoc used HP81 only for their "B-Series" machines which were produced around 1993-95. They then went to the "J-Series" which used R-404A and on to the "Q" and now "S" machines.

    The big deal about HP 81 was as Dave mentioned is the higher discharge temperatures and Manitowoc wanted to see 170+ Deg F during the freeze cycle to buildup enough heat in the system for a proper harvest. I experimented recently with an old "B-600" using HP81 and then switching to HP 80. The HP81 discharge temps were generally 20 Deg F higher than the HP80 and the harvest time with HP 81 was 1.5 minutes vs almost 2.5 minutes with the HP80. Interestingly enough, the HP81 ran a lower evaporator SH but resulted in a higher compressor discharge temperature.

    My overall opinion is that it was probably easier to get Dupont to manufacture a special refrigerant than to engineer a machine that actually worked well on the generally accepted R502 replacement refrigerant.

    As far as the old R12 machines goes, R401A (MP39) was in fact Manitowoc's designated interim replacement refrigerant and I recall having to swap TXVs on the 400s (it was actually adjustable). I don't remember them requiring an oil change even back when Dupont said it was necessary.

  11. #11
    Join Date
    Oct 2003
    Location
    Valdosta Ga
    Posts
    847
    Post Likes

    Wink R-22

    If you are going to change the txv might as well change it to r-22 the freon works well in ice machines and you can probly find a old a/c compressor cheaper than getting freon that you will not ever use.

  12. #12
    Join Date
    Oct 2003
    Location
    Valdosta Ga
    Posts
    847
    Post Likes

    also

    If the compressor has already been swaped it may work with R-22 alot of retros were doing this.

  13. #13
    Join Date
    Apr 2004
    Posts
    8
    Post Likes
    I used 401-a in a manotowoc ice machine. It was recommended because we couldn't get the original compressor that used r-12. Anyway since I made the changeover I have rebuilt all of our ice machines and recharged with hot shot. (414-b) They all work fine.

  14. #14
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes

    Hmm Re: R-22

    Originally posted by bzzline
    If you are going to change the txv might as well change it to r-22 the freon works well in ice machines and you can probly find a old a/c compressor cheaper than getting freon that you will not ever use.
    I wouldn't recommend putting an "old" compressor of any variety in, much less one that was designed for a 40 degree evap.

    Fastest way to get your Referhack merit badge.

  15. #15
    Join Date
    Oct 2003
    Location
    Valdosta Ga
    Posts
    847
    Post Likes

    old ice

    I bought some mp39 for a Ice machine that cost just about twice what I could have paid for a brand new window unit (an used the compressor out of) and would have at least a fan motor left over I could have sold by now.


  16. #16
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes

    Re: old ice

    Originally posted by bzzline
    I bought some mp39 for a Ice machine that cost just about twice what I could have paid for a brand new window unit (an used the compressor out of) and would have at least a fan motor left over I could have sold by now.

    If you're selling these Frankenstein monsters, you're ripping off whoever buys one.

  17. #17
    Join Date
    Oct 2003
    Location
    Valdosta Ga
    Posts
    847
    Post Likes

    Its just a option

    When you cannot go back with OEM just as well leave it alone.

  18. #18
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes
    Why couldn't you go back with OEM???

    Unless it's some oddball, completely out of production unit, the right parts are available for essentially all of them.

    A rose by any other name, and

    Hacking is hacking is hacking is hacking.

  19. #19
    Join Date
    Oct 2003
    Location
    Valdosta Ga
    Posts
    847
    Post Likes

    options under $200

    Who wants to put $1300 into a old r-12 anything. If the customer is using outdated equipment it is probly not because he wants to.
    If I want to help the little guy thats fine call me a hacker

  20. #20
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,218
    Post Likes
    That's the oldest hack excuse in the hack manual.

    If the guy can't afford to do business, so what?

    Someone else might come along and buy him out, seeing as how his financial condition is so fragile, and get stuck with one of your POS nightmares, and wind up having to buy a new machine because no one can figure out why it won't work right.

    How many btuh are these window unit rotaries rated at at a zero degree evap, anyway???? I know, you don't know.

    You don't know, because it is 30 degrees out of their operating envelope. But, that doesn't matter to YOU, because it's cheap, and what could POSSIBLY go wrong with it??????????

    How long is your warranty on something like this, BTW?

    If you're gonna Do something like that, you oughtta spray paint your name and number on the front of it, so know one else winds up in a living nightmare.


+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •