Results 1 to 12 of 12
    Mar 2010
    Normal Delta_T For Heat Pump System?
    What is the normally accepted range Delta T between supply & return on the heating side of a heat pump system? My new system was giving about 22F degrees when it was low 50's outside ambient, but barley gives a max delta of 10F when its low 40's outside. Thanks!
    Dry as a bone Tucson
    switch the fan to auto and system to heat
    John Proctor
    Watchman Nee
    Sounds very low. Typical 20+ at 30 out, close to 30 degree rise at 50 out with proper airflow.
    Sep 2009
    Iowa
    with a bryant h/p and an electric air handler with no heat strips running i was getting a 32 degree F split with a 20 degree F temp. outside
    Dec 2009
    McCook NE
    My Nordyne will give me 20.3° at 17°.
    In a boiler room
    See the key words; Proper Airflow.
    Worry is a really gross misuse of one's imagination. -- PHM
    Dec 2009
    Seattle, Wa.
    I had a new Lennox G71MPP furnace and XP14-042 heat pump installed a month or so ago. The Delta T at 55 degrees exterior temperature with the heat pump running was 40.
    Oct 2005
    Pacific Northwest
    Quote Originally Posted by BBDartCA View Post
    Call 'em back!
    What's you model numbers?
    Jun 2007
    The Twilight Zone
    Tech Operating Data for my 3-ton, 14 SEER, 9 HSPF pump:
    Ambient-------Temp after indoor coil
    Temp-------(based on 70F return air temp)
    60F---------------105.8F
    50F---------------101.5
    40F---------------97.1
    30F---------------93.4
    20F---------------89.9
    10F---------------86.2
    0F----------------82.6
    Take care.
    Quote Originally Posted by gary_g View Post
    Ambient-------Temp after indoor coilambient usually refers to outdoor temp unless otherwise specified
    if I were to read CAREFULLY you are saying that, for example, an ambient(outdoor) temp of 0*F with a return air temp of 70* gives you a supply temp of 82.6*F or 12.6* temp rise/delta T
    Take care.
    Jun 2007
    The Twilight Zone
    Quote Originally Posted by pacnw View Post
    You are reading the columns incorrectly.
    Ambient temps are in the column going from 60F to 0F, with the corresponding coil temp in the column next to each ambient temp.