    keep the vent valve closed

  2. #67
    Join Date
    Mar 2007
    Posts
    3,108
    If migration due to water flow or the room's temperature control is the issue, maybe isolation valves or a different thermostat setting are the answer...?
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

  3. #68
    Join Date
    Aug 2004
    Location
    DFW
    Posts
    147
    Do you have condensor water regulating valves controlled by the ch530? Maybe settings are different between the 2 machines. Could it be that the chiller having the issue is starting up under different conditions than the other? If the condensor water regulating valve is N.O. vs N.C in the off state. All the rthds I have started up since 2009 have had this valve. I was thinking that they made this required.

  4. #69
    Join Date
    Aug 2004
    Location
    DFW
    Posts
    147
    Quote Originally Posted by servicetrane View Post
    keep the vent valve closed
    Say What?
    The valve is closed during shipping. It is opened at start up.

  5. #70
    Join Date
    Oct 2006
    Location
    Central Texas
    Posts
    632
    Quote Originally Posted by svc View Post
    Do you have condensor water regulating valves controlled by the ch530? Maybe settings are different between the 2 machines. Could it be that the chiller having the issue is starting up under different conditions than the other? If the condensor water regulating valve is N.O. vs N.C in the off state. All the rthds I have started up since 2009 have had this valve. I was thinking that they made this required.
    I've only heard of the regulating valve as an option, same as the RTHC.
    Sic Semper Tyrannis.

  6. #71
    Join Date
    Aug 2004
    Location
    DFW
    Posts
    147
    I looked it up. You are right it is in option! However it would be a requirement under certain conditions for the chiller to operate within its design envelope. RTHD chillers rely on differential pressure between the compressor discharge and suction to move oil through the compressor rotors and bearings for cooling and lubrication. It also requires an oil pressure differential in order to load the compressor. Lower temperature and pressure in the condenser (and higher temperature and pressure in the evaporator) can reduce the chiller’s differential pressure below the minimum required for proper cooling, lubrication, and loading. The chiller is protected from compressor damage by the CH530 control system. However, inadequate pressure differential will keep the chiller from operating. The most effective way to maintain the required differential pressure during chiller startup and operation is to apply condenser water temperature control.

  7. #72
    Join Date
    Oct 2006
    Location
    Central Texas
    Posts
    632
    Quote Originally Posted by svc View Post
    I looked it up. You are right it is in option! However it would be a requirement under certain conditions for the chiller to operate within its design envelope. RTHD chillers rely on differential pressure between the compressor discharge and suction to move oil through the compressor rotors and bearings for cooling and lubrication. It also requires an oil pressure differential in order to load the compressor. Lower temperature and pressure in the condenser (and higher temperature and pressure in the evaporator) can reduce the chiller’s differential pressure below the minimum required for proper cooling, lubrication, and loading. The chiller is protected from compressor damage by the CH530 control system. However, inadequate pressure differential will keep the chiller from operating. The most effective way to maintain the required differential pressure during chiller startup and operation is to apply condenser water temperature control.
    Agreed 100%. The Carrier 30HXCs are the same way, the machine is not sold with a regulating valve, but one can be field installed, set-up, & the chiller will control the valve. People really need to have to have good control of their towers w/ these machines.
    Sic Semper Tyrannis.

  8. #73
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    180
    Trane recomends controling the condenser bypass based on the pressure difference between the condenser and evaporator. A minimum of 23# delt-p between the condenser and evaporator needs to be maintained for proper oil flow. The condenser water needs to be 17deg higher than the chill water with in 2 min of startup. A 25deg. deta-t must be maintained.
    Attached Files Attached Files

  9. #74
    try setting your delta P to 240kpa (2vdc) min and 480kpa (10vdc) max for your cond regulating valve

  10. #75
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,087

    control

    yep., there are 5 reasons why this machine need this control
    and 4 methods of control.

    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

Page 6 of 6 FirstFirst 123456

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event