    Hey Cumulus, how did you make out on this one? Just curious if you had found the issue.

  2. #41
    Join Date
    Nov 2009
    Location
    USA
    Posts
    26
    Quote Originally Posted by brooklyntech View Post
    Dont know if this helps-but that float in the gas pump was originally some type of plastic ball (or other tyoe of material), but we had similar issue, and after cutting open a gas pump we found that little ball had melted or warped from the heat of brazin all the line goin into gas pump. I cant remembr if that was on an rthc or rthd? hmmm. I'll have to ask.
    The origional check valve was an issue. I remember attending a warantee meeting when the machine was still in development, and none of us liked the check valve design. I did change one which has the symptom you described. Just make sure the check is seating on the drain cycle by checking temperatures when in the fill & drain modes.

  3. #42
    Join Date
    Jul 2009
    Location
    Michigan
    Posts
    103

    RTHD & RTWD

    Is there any consensus that the RTWD will have all the same issues as the RTHD?

  4. #43
    Join Date
    Nov 2009
    Location
    USA
    Posts
    26
    The early issues on the RTHD were resolved, so I would suspect the RTWD would be ok overall.

  5. #44
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,067
    Quote Originally Posted by graham View Post
    Another thought , you say the gas pump is working . How do you know ? just because the solenoids are alternating does mean its working ,the check valve could be blocked /stuck etc.
    Did you hook up you laptop and run trendview to check "The Heartbeat" this is proof that the gas pump is working .

    is this program the techviev program that u are talking about and also is this the only way to tell if the gas pump is working? how can one tell if the solenoids are leaking by., i hear that that can b a problem as well ., check valve can b an issue thought huh., can the gas pump be isolated to do the repairs?

  6. #45
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,067

    Talking

    Quote Originally Posted by maxpower View Post
    If you had some contact info in your profile you could receive some more info you could read..
    hey bud u think i can gete an email about this as well ., i am biddibg on this machine and i want to b prepared., thanks`

  7. #46
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    466
    review this bulletin
    RTHD/RTHC
    Gas Pump Solenoid Leak
    Order Number: RLC-SVC12A-EN

  8. #47
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,067
    Quote Originally Posted by servicetrane View Post
    review this bulletin
    RTHD/RTHC
    Gas Pump Solenoid Leak
    Order Number: RLC-SVC12A-EN

    i went to trane.com under lit search., cant find it .,

  9. #48
    Join Date
    Mar 2007
    Posts
    3,103
    I saw the service bulletin about the lines to the liquid level canister being sloped, there was also one that said something about if the insulation fails or falls off or whatever on the liquid pipe to the canister, "rapid and violent boiling" of the refrigerant caused by high ambients outdoors and inside mechanical rooms can throw off the float.

    I pulled out an old float style liquid level sensor recently and upon looking at it, considering that the thing is surrounded by refrigerant and some oil and is not subjected to any force, I don't see how it could ever fail, or stick, or do anything other than what it was designed to do...

    The RTWD has CHHP compressors, which are a different animal than the CHHC compressor you have on an RTHD.
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

  10. #49
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    466
    oil prevents a good reading of liquid level sensor in the RTAC units a high level of oil causes many problems including liquid level sensor

  11. #50
    Join Date
    Mar 2007
    Posts
    3,103
    Quote Originally Posted by servicetrane View Post
    oil prevents a good reading of liquid level sensor in the RTAC units a high level of oil causes many problems including liquid level sensor
    I can see how having excess oil in the evaporator would affect the reading of the liquid level sensor, but what I was talking about was a mechanical failure of the float itself.
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

  12. #51
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,250
    Quote Originally Posted by mlkwal1 View Post
    i went to trane.com under lit search., cant find it .,
    because the lit number he gave you was a 'Confidential Service Bulletin'

    look for RLC-SVB12A-EN
    my 1st time jumping out of a plane...http://youtu.be/Kv38G0MHsGo

  13. #52
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,067

    Thumbs up

    Quote Originally Posted by jayguy View Post
    because the lit number he gave you was a 'Confidential Service Bulletin'

    look for RLC-SVB12A-EN
    ok thanks

Page 4 of 6 FirstFirst 123456 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event