10-04-2010, 10:34 AM #66
keep the vent valve closed
-
10-04-2010, 08:39 PM #67
If migration due to water flow or the room's temperature control is the issue, maybe isolation valves or a different thermostat setting are the answer...?
Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.
"It's called the american dream because you have to be asleep to believe it" -George Carlin
"A nation of sheep begets a government of wolves" -Edward R. Murrow
"I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney
Buy american made goods & support locally owned businesses!
-
10-23-2010, 08:42 PM #68
Member
- Join Date
- Aug 2004
- Location
- DFW
- Posts
- 147
Do you have condensor water regulating valves controlled by the ch530? Maybe settings are different between the 2 machines. Could it be that the chiller having the issue is starting up under different conditions than the other? If the condensor water regulating valve is N.O. vs N.C in the off state. All the rthds I have started up since 2009 have had this valve. I was thinking that they made this required.
-
10-23-2010, 08:44 PM #69
Member
- Join Date
- Aug 2004
- Location
- DFW
- Posts
- 147
-
10-24-2010, 05:26 PM #70
-
10-24-2010, 09:03 PM #71
Member
- Join Date
- Aug 2004
- Location
- DFW
- Posts
- 147
I looked it up. You are right it is in option! However it would be a requirement under certain conditions for the chiller to operate within its design envelope. RTHD chillers rely on differential pressure between the compressor discharge and suction to move oil through the compressor rotors and bearings for cooling and lubrication. It also requires an oil pressure differential in order to load the compressor. Lower temperature and pressure in the condenser (and higher temperature and pressure in the evaporator) can reduce the chiller’s differential pressure below the minimum required for proper cooling, lubrication, and loading. The chiller is protected from compressor damage by the CH530 control system. However, inadequate pressure differential will keep the chiller from operating. The most effective way to maintain the required differential pressure during chiller startup and operation is to apply condenser water temperature control.
-
10-24-2010, 09:25 PM #72Sic Semper Tyrannis.
-
10-26-2010, 01:38 PM #73
Professional Member
- Join Date
- Mar 2010
- Location
- Va.
- Posts
- 178
Trane recomends controling the condenser bypass based on the pressure difference between the condenser and evaporator. A minimum of 23# delt-p between the condenser and evaporator needs to be maintained for proper oil flow. The condenser water needs to be 17deg higher than the chill water with in 2 min of startup. A 25deg. deta-t must be maintained.
-
10-28-2010, 05:53 AM #74
New Guest
- Join Date
- Oct 2010
- Posts
- 2
try setting your delta P to 240kpa (2vdc) min and 480kpa (10vdc) max for your cond regulating valve
-
10-28-2010, 10:29 PM #75
control
yep., there are 5 reasons why this machine need this control
and 4 methods of control.