    06E Oil pressure lockout_NOT!

    Anyone run into a Carrier 38AKS 028 -601 running the compressor with a net oil 0f 2psig and not tripping the oil saftey?
    This compressor was so noisy I wasnt sure what head to pull first to inspect for damage.
    I decided to condem the compressor all together as their is no way to tell how long it ran without lube.
    Also noticed the resistors on the control module were overheated. I checked acroos the input for the ops and the switch was still closed after 4min of compressor runtime below 5psig.
    Attached Images Attached Images    
    If you cant fix it right, try again.

  2. #2
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,725
    Oil in the sightglass?
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  3. #3
    Join Date
    Jun 2001
    Location
    Northwest Indiana
    Posts
    1,321
    Quote Originally Posted by thegoodlistener View Post
    Oil in the sightglass?
    A little less than 1/8" "no agitation"
    If you cant fix it right, try again.

  4. #4
    Join Date
    Jun 2001
    Location
    Northwest Indiana
    Posts
    1,321
    Split (upper,lower) DX coils. They are both plugged solid! Condensor coil also plugged solid! Return fan belts loose and drive motor pullet open too far with the belts riding low.
    All contributing to this failure, this store stops maintenance 2 yrs ago and wonder why.
    If you cant fix it right, try again.

  5. #5
    Join Date
    Dec 2009
    Location
    Southern US
    Posts
    504
    We have had several natiional accounts stop maintenance programs in tghe last few years. Some have restarted when their repair costs have become excessive from just the type of issues you found.
    I'm good at making things cold...You can ask my first two wives!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event